the figures are given in BS7671 without the 80% correction factor. these are what i use. in winter when we are measuring @3 deg.C, not 20, should we then apply another correction?
dont know. just thought you had to apply appendix 14
 
i know your not in Britain, but if you were, surely you'd have to work to BS7671 requirements?

wouldn't not meeting these requirements constitute a C2

A C2 would be the code applied to a potentially dangerous fault found on an EICR, there is no such thing on an EIC.
If he has used values other than those in the books and recorded this deviation as part of the installations documentation then as long as the testing proves that the circuit is within those values there is no problem. Bs7671 is not the be all and end all of electrical installation!
 
Perhaps i should of also pointed out that the typical Zs values measured on our projects will meet and exceed anything that's presently deemed as max Zs values...
 
A C2 would be the code applied to a potentially dangerous fault found on an EICR, there is no such thing on an EIC.
If he has used values other than those in the books and recorded this deviation as part of the installations documentation then as long as the testing proves that the circuit is within those values there is no problem. Bs7671 is not the be all and end all of electrical installation!
doesn't an earth loop impedance value greater than that required warrant a potentially dangerous fault, ergo C2?

which other values apart from the manufactures are there?
 
doesn't an earth loop impedance value greater than that required warrant a potentially dangerous fault, ergo C2?

Been absolutely fine for god knows how many years, so what's suddenly changed to make previously stated accepted values now ''Potentially Dangerous''?? Answer '' ...NOTHING!!
 
Been absolutely fine for god knows how many years, so what's suddenly changed to make previously stated accepted values now ''Potentially Dangerous''?? Answer '' ...NOTHING!!
don't quite follow u eng, nothings changed! just saying that exceeding max zs values as given in BS7671 is a C2 is it not? or is it all FINE!!!!!!
 
and just to muddy the waters further, manufacturers data could well give a higher figure. as long as the MCB/fuse will operate within the specified time, then bob's your dad's brother.
 
so, you work out your fault current which is dependant upon impedance (Zs) then look up the time characteristics data for disconnection time.
 
A C2 would be the code applied to a potentially dangerous fault found on an EICR, there is no such thing on an EIC.
If he has used values other than those in the books and recorded this deviation as part of the installations documentation then as long as the testing proves that the circuit is within those values there is no problem. Bs7671 is not the be all and end all of electrical installation!

Electrical Installation Certificate EIC
 
the time/current graphs in BS7671 are generic. different makes of OCPDs may well give different (better) figures.
 
don't quite follow u eng, nothings changed! just saying that exceeding max zs values as given in BS7671 is a C2 is it not? or is it all FINE!!!!!!

Think about it for a second, previously stated max Zs values satisfied ADS requirements, so how can you, (or should i say they) now say that they Don't??

Of all the things that needed sorting out within BS7671, max Zs values wasn't and still isn't one of them. A totally wasted Amendment opportunity all round, when you also take into account the plastic/metal CU farce!!!
 

Reply to max zs table in the osg in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
864

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
254
  • Question
This potential client seems to be making progress in terms of being interested in proper chargers and answering my query questions. I have also...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top