Hi
Is the max Zs values of a bs3871 the same as a BS 60898 mcb as 60898 replaced the 3871?
thanks
Is the max Zs values of a bs3871 the same as a BS 60898 mcb as 60898 replaced the 3871?
thanks
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Max Zs values of bs 3871 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
No.
They are essentially 2 different breakers. 3871's were type 1,2 & 3 whereas 60898's are B,C & D. The only ones that are the same are type 3/C. Page 103 in the OSG has the info you need.