Is the max Zs values of a bs3871 the same as a BS 60898 mcb as 60898 replaced the 3871?

thanks
 
No.

They are essentially 2 different breakers. 3871's were type 1,2 & 3 whereas 60898's are B,C & D. The only ones that are the same are type 3/C. Page 103 in the OSG has the info you need.
 
No.

They are essentially 2 different breakers. 3871's were type 1,2 & 3 whereas 60898's are B,C & D. The only ones that are the same are type 3/C. Page 103 in the OSG has the info you need.

Or in the event of having no tables to hand, use simple Ohms Law!

We all know that R = V/I, and know that V is 230V.

Type 1 MCB's trip instantaneously (0.1 s) at 4 times the rated current, type 2 trip at 7 times the rated current and type 3 trip at 10 times.

Therefore, if we had a 10A type 1, we would have R=V/I=230/(4x10)=230/40=5.75 ohms maximum earth fault loop impedance.

Always worth knowing the maths if you don't always have the tables, although it's not so easy with fuses as you need the current curve graphs....
 
And remember that the OSG and GN3 values are at the 80% values, not necessarily the maximum permitted by BS7671... Although that point is still quite contentious!
 
Print this laminate it and put it in you folder

Ok what happened to the attach option
 
Last edited by a moderator:

Reply to Max Zs values of bs 3871 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

It isn't OK as it is otherwise it wouldn't have been coded C2 on an EICR.
Replies
9
Views
921
davesparks
D
Thanks for that, good line of thought. My take is that safety is about protection of life/people/livestock hence the earth thing and protection of...
Replies
31
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top