In theory, a max impedance of 1666 on a 230v nominal supply does give you a current of slightly less than 5x but vastly exceeds 1x so it shouldn't matter..... but ..... we press the test button on RCD's for a reason whereas ADS just dependably sits there.
But frankly if you're even anywhere close to working with numbers that high then you've got bigger issues anyway, not least of which is Vd.
Agree so why would anyone wanna put 1666 in the column regarding TN Systems
Especially when the actual measured Zs is going to be a low Ohm reading
If ADS is satisfied by the mcb then use the mcb if ADS is satisfied by the RCD then use that.
If ADS is satisfied by the mcb then use the mcb If ADS is satisfied by the RCD then use that.
I think the technical argument there is that the RCD would be additional protection not basic protection under ADS??
411.x states in several places that where an RCD is used for additional protection it needs to conform to the same ADS times as for Zs measured circuts (paraphrasing!). HOWEVER, 415.1.2. tells us that "The use of RCDs is not recognised as a sole means of protection and does not obviate the need to apply one of the protective measures specified in Sections 411 to 414".
However again, 411.8.3 eventually tells us "where fault protection is provided by an RCD, the product of the rated residual operating current (I∆n) in amperes and the Earth Fault Loop Impedence in ohms shall not exceed 50V". Which as we all know is where we get our magical 1667 * 0.03 = 50v.
On that basis, I think it's probably (as I answer my own theorem...) more technically correct to use the 1667Ω figure in the max Zs column. Still doesn't mean I like it!!! If one of us could be arsed to pick up a GN3 we'd probably find there's a note in there somewhere that clarifies this!! 😂
415.1.2 just means if you have an EN 61008 device then you must have an overcurrent device incorporated into it, l believe.
Where an mcb cannot satisfy ADS it is perfectly acceptable to use an RCD and in some circumstances it will provide additional and fault protection.
415.1.2 The use of RCDs is not recognized as a sole means of protection and does not obviate the need to apply one of the protective measures specified in Sections 411 to 414.
I think it means that we cannot rely on an RCD alone as a complete protective measure against electric shock.
There are:
411 - Protective measure: ADS
412 - Protective measure: Double/reinforced insulation
413 - Protective measure: Electrical separation
414 - Protective measure: ELV/SELV/PELV,
but there is no section called Protective measure: RCD. This, I believe, is what 415.1.2 is reminding us.
Why? Because that is the maximum Zs for the circuit. The RCD doesn't know or care whether the earthing arrangement is TN or TT, or if you prefer the values for MCB, it's going to trip anyway, and that is its max Zs.
Also: Because where a circuit is protected by an RCD, there is no need to provide a Zs reading, either measured or calculated. Once you have proved that the RCD works, and that the CPC is continuous by either R2 or R1+R2, then you have met disconnection times.
I find this odd but it is the way of things now. If you have your R1 + R2 you may as well put in the Zs anyway by way of calculation.
While that is technically true it is a path that leads to ECIR by socket tester results - wet string below 1.6k ohm? Pass!
My own view is you should be looking at an installation to see if it is in good safe condition, and if you are not meeting Zs on a TN system it starts to ring alarm bells. It could just be a long cable (or high current distribution circuit and high-ish supply Ze) so it is healthy but reliant on the RCD for ADS within the allocated time, or it could be an indication that something is badly corroded and might not survive more than one fault or a bit of vibration before it goes open and the person becomes the path for ADS current to trip things.
Also I get a touch nervous at the use of a single RCD for your ADS. They are rarely tested outside of ECIRs (even if they should be done twice a year or more), and the electronics is many times more complex than the thermal-magnetic trip of the MCB side of things. Yes, it is perfectly within the regs, but having seen the odd failed RCD in the past I would really prefer to have two RCDs (delay incomer & additional 30mA ones) so there is no single point of failure in ADS if something like TT earthing made it the only practical means of achieving ADS.
While I hear what you're saying, I think that focussing on Zs is the wrong thing to focus on, when time can be better spent on other parts of I and T.
A measured Zs value will prove only one thing - that the disconnection times are met. True, it might give a loose indication that something is wrong, but then again it might not. For example, a measured Zs of 5 ohms on a B6 lighting circuit is well within Zs limits, but there is something amiss if you're getting this in the average domestic property. Or perhaps an immersion heater circuit gives a very nice low Zs, but is using the pipework as an earth.
It doesn't prove that the CPC is continuous, or that the L or N don't have loose connections in them, or give a circuit length, or even that the polarity is correct. These things are much better tested for by continuity.
Yes, sometimes RCDs do fail. However, even if it should fail, it is very likely that the MCB will disconnect anyway, seeing as we calculate max Zs based on the absolute upper limit of the device and a voltage that is far lower than normally encountered.
Some interesting comments!
Also a high Zs could be caused by RCD uplift, especially with older RCD's.
I put the Max Zs in as that of the 60898 max reading for RcBO's, as above they can fail and then you are reliant on the MCB side of the device for protection.
Sy
But splutter splutter, why isn't a Zs generally necessary? Not saying you're wrong but curious to know your reasoning as to why you are not really bothered about ensuring the MCB L-N fault is within ADS requirements?
cliffed
Worcester
United Kingdom
Electrical Engineer (Qualified)
Zs measurements in the Cert column
Thread Tags
cliffed,
Vortigern,
TrueNAS JBOD Storage Server