But splutter splutter, why isn't a Zs generally necessary? Not saying you're wrong but curious to know your reasoning as to why you are not really bothered about ensuring the MCB L-N fault is within ADS requirements?
There are no requirements in ADS to disconnect for a L-N fault.

ADS is section 411, in chapter 41: protection against electric shock. L to N faults don't generally cause electric shock, as they cause no rise in voltage on exposed conductive parts, so the disconnection times in 411 do not apply. There are other reasons to disconnect (adiabatic), but these faults aren't required to meet the times tabled in 41.1

411.3.2.1
Except as provided by Regulation 411.3.2.5, a protective device shall automatically interrupt the supply to the line conductor of a circuit or equipment in the event of a fault of negligible impedance between the line conductor and an exposed-conductive-part or a protective conductor in the circuit or equipment within the disconnection time required by Regulation 411.3.2.2, 411.3.2.3 or 411.3.2.4.

(* L to N faults don't generally cause electric shock, as they cause no rise in voltage on exposed conductive parts: actually, I believe that this isn't the full story. I believe that a L-N fault would see a rise in voltage on the earthing system for a TN-C-S earthing arrangement, the E and N being connected at the cutout.

However, a fault so low that it failed to disconnect the protective device quickly would be a long way downstream of the cutout. I believe that much of the voltage would have dropped between the fault and the cutout, so the rise on the earthing system would be low.)
 
Thanks for that, good line of thought. My take is that safety is about protection of life/people/livestock hence the earth thing and protection of property. While I certainly agree that usually L-N faults don't normally present danger in terms of electrocution/shock there is a risk of fire/damage to property and hence life if someones in the house at the time of a fire. Therefore I tend to keep an eye on PSSC for the above reasons so I can feel assured that in the event of a fault safety to property etc. is assured. I note your point about N-E connection at the cut-out and often ponder on that and as we know a broken neutral exterior to the site means a live earth and so on. I try not to over-think it all though. Just being as careful as I know how. In any event when doing a Zs L-E the L-N is automatic and presented on the meter so it is not a big deal to note it.
 

Reply to Zs measurements in the Cert column in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
852

Similar threads

  • Question
Yea all out circuits were disconnected & Rcd ramped tested Think this will be the right way forward,with EL clamp meter Cheers have a nice Christmas 😎
Replies
2
Views
1K
  • Question
Just re-read the OP's post and it is an existing 5C SWA so presumably a 3P supply. For 40A and 150m you are seeing 6.6V drop or 1.65% of 400V 3P...
Replies
8
Views
881

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top