T
ted26
Does anyone know the maximum cable length that can be used for a ring circuit using 2.5 t+e with a 32amp breaker?
the OSG has a table in there giving maxium cable lengths for cable size but as I haven't got mine with me can tell you which one, sure if one of the other lads are following this thread they can give you the table reference
if the area covered is 100m2 then does that mean that the cable can be 40 meters long end to end (ie going around a square room that is 10x10m meaning it would cover 40m end to end?
subject to all other criteria being met
in a 10X10 meter square what about the drops or rises.....if the rooms got a 5 meter celing hight and your drop is from there then how big would your ring main be...
its all about cable resistance and what protection you have and the temperature and the insulation around the cable.....
if i were you id look into some cable calcs....they are a wonder to behold..
I atually searched and found a reference earlier which said something like 98m for 2.5 and 178m for 4.0
this i think must be the maximum for each and could be lower depending on other influences
what about the drops/rises to sockets. as vito says, have to meet Zs less than 1.2 for a 32A type MCB, so knowing Ze and the resistance of R1 and R2 per 100m each, you can work it out
You are right but have forgot more than i now know!! been working easy for 10 years and need to refresh my electrical installation theory.
anyway thanks for any help from all
Maximum cable length
Australia
ted26,
JUD,