Maximum Zs Value Exceeded | on ElectriciansForums

Discuss Maximum Zs Value Exceeded in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jan 13, 2021
Messages
2
Reaction score
0
Location
Leeds
Hi

I have recently done some testing on an installation. A submain is fed from a B50 mcb and has a zs of 1.10ohms. The maximum for this is 0.87. The cable supplying the submain is a 25mm 2 core swa with the armourings used as the cpc and is roughly a 70m run. Both glands and earth leads have been checked and are okay.

Would it be viable to fit a 300ma rcd to protect this circuit as the disconnection time cannot be achieved. The problem I have is the building supplied by this has two large heaters and a number of vacuums and there is an earth leakage of around 150ma.

Each circuit in the submain has individual 30ma protection.

Upgrading the cable/running a separate earth alongside the swa would not be possible due to the nature of site.
 
Hi

I have recently done some testing on an installation. A submain is fed from a B50 mcb and has a zs of 1.10ohms. The maximum for this is 0.87. The cable supplying the submain is a 25mm 2 core swa with the armourings used as the cpc and is roughly a 70m run. Both glands and earth leads have been checked and are okay.

Would it be viable to fit a 300ma rcd to protect this circuit as the disconnection time cannot be achieved. The problem I have is the building supplied by this has two large heaters and a number of vacuums and there is an earth leakage of around 150ma.

Each circuit in the submain has individual 30ma protection.

Upgrading the cable/running a separate earth alongside the swa would not be possible due to the nature of site.
Yes an upfront time delayed rcd is an option.
What is the Ze ?
How many Rcd circuits are there being supplied by this sub main. ?
 
Last edited:
What readings were you expecting for the cable prior to testing?
What is the make of the protective device?
Is there any previous paperwork [test or design] for that distribution leg?

By a quick estimation (estimation because no figures for resistance with me for the armour so somewhat ball-park) and based on 20 C temperature at time of test that R1 / R2 would seem to be too high for the length of run on a 25mm cable.
 
Last edited:

Reply to Maximum Zs Value Exceeded in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Merry Xmas to all :D
    • Friendly
    • Like
Replies
8
Views
428
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
743
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
580
  • Question
All the lamp post cutouts I've ever seen have a twin swa gland plate built in to the base.
Replies
2
Views
695
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top