Hey I had a callout referred by a lad working for me yesterday where one of the old dimplex CXL I think it is storage heater with an on peak convector heater built in had a fault and took out the property supply.

He had attended the call and said that the B16 Hager at the board had not tripped at off peak or on peak but found that in the riser to the other flats that the B63 Hager had indeed tripped next to the 4 pole switch and so taken the entire on peak / general service feed to the flat consumer unit out.

I would've thought that if there was a high enough fault current or short that it would have taken the 16A before the 63A at source ?

I will be going there tomorrow but just wondering if anyone has had an issue such as this before ? Thanks,
 
Discrimination between mcb's is typically hard to achieve. Having two in series like you have on this job is poor design. IIRC the the upstream MCB would roughly need a current rating of around 100A to discriminate with the 16A MCB if they are both type B...It would be better to have a fuse as the protective device for the distribution circuit..I would discuss the benefits of changing what ever the existing set up is to a switch fuse.
 
Discrimination between mcb's is typically hard to achieve. Having two in series like you have on this job is poor design. IIRC the the upstream MCB would roughly need a current rating of around 100A to discriminate with the 16A MCB if they are both type B...It would be better to have a fuse as the protective device for the distribution circuit..I would discuss the benefits of changing what ever the existing set up is to a switch fuse.
Thanks Lee, seems to be a very used method over here unfortunately, 4 pole main switch controlling both supplies and then a 63A mcb each side isolating the line to the boards. He said consumer unit is a mess too and apparently a weird kind of stranded mains cable so I think must be split concentric to the flat board. Thanks again
 
Just for future knowledge, you would need a 160amp MCCB to give full discrimination against a standard MCB board with max 63amp ratings, anything below that only gives partial and at the fault currents we tend to see then partial means pot luck as either mcb is likely to trip first, if I recall a 63amp mcb only gives full discrimination on 6 and 10amp mcb's if fault current low enough, again above that and you might as well flip a coin as to which series device will trip first.
 
Last edited by a moderator:
Just for future knowledge, you would need a 160amp MCCB to give full discrimination against a standard MCB board with max 63amp ratings, anything below that only gives partial and at the fault currents we tend to see then partial means pot luck as either mcb is likely to trip first, if I recall a 63amp mcb only gives full discrimination on 6 and 10amp mcb's, again above that and you might as well flip a coin as to which series device will trip first.
Brilliant thanks you guys. Checked today, stripped and cleaned and tested elements etc. All alright today !
 
yes partial discrimination but what good is that ?
Partial discrimination can be fine if your fault current is sufficiently low enough but like my post said, in most cases the fault current is large enough to mean it's a game of pot luck unless of course you have full discrimination, Ill ask again can you cite any charts/info to back up your claim that a 63 amp mcb will not fully discriminate to a 6 amp - I have some very useful discrimination charts from that say otherwise.
 
No two BS EN 60898 circuit breakers of any rating will reliably discriminate.
Unless you have the manufacturers assurance that they will, the above statement is a broad generalisation, quality of product can offer better discrimination, in reflection I should have made that clear in my post but a low fault current means you cannot make a sweeping statement like has been although like I said under your average fault current then we have partial.
 
Last edited by a moderator:

Reply to MCB discrimination ... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Part III:). I think I have clarity-having spoken to my electrician who installed my heaters, he said that the part of my fuseboard that is...
2 3 4
Replies
52
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top