These things are blooming huge!

[ElectriciansForums.net] MCB, RCD & AFDD all in one


Oh and ÂŁ170 :eek:
 
Seems these things are elusive.

Eaton are quoting ÂŁ160 per combined unit and a 16 day lead time.

They also do not do 3 phase units.

??????
Also according to the NIC presenters, ADDS will not work on a RFC, they didn't give a very good explanation on the film they produced, but the fact that AFDDs won't work on a RFC according to them was something that stuck in my mind.
 
Whilst AFD's don't detect series arc faults on a ring final cct that mode of fault is not as dangerous on a ring because of the parallel path available for the load current so it's kinda swings and roundabouts....
 
Things can be in the regs even without a tester - after all there's never been a tester for the magnetic or thermal parts of an MCB/RCBO, only for the residual current part. Dame goes for fuses for that matter. so we have no idea if they still work when doing inspection and testing.
 
Things can be in the regs even without a tester - after all there's never been a tester for the magnetic or thermal parts of an MCB/RCBO, only for the residual current part. Dame goes for fuses for that matter. so we have no idea if they still work when doing inspection and testing.

But if a fuse blows or an MCB trips you have test equipment to diagnose the fault quickly and reliably every time.

No such thing with these devices, one might keep tripping due to a natural arc in a circuit (something switching). How do you fault find that.... just start replacing parts at an unnecessary cost.
 

Reply to MCB, RCD & AFDD all in one in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
426
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
790
  • Question
This charger doesn't support rear entry from the looks, only bottom entry, hence that. Unless they make a white sheathed SWA, I would still need...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top