Morsey

-
Joined
Nov 26, 2018
Messages
7
Reaction score
9
Location
Wilts
Evening all
Let’s see if anyone can solve this one.
Recently wired a new extension. Today connected up ring circuit to 32amp mcb, all relevant dead testing done ir +999mohms and ring continuity.28 .28 .48. So all good turn mcb on and pop it trips off. Rechecked testing removed sockets just to double check for any small nicks etc all fine. Reconnect and turn on all seems fine. Hour or so later same problem. Replaced mcb all fine. Hour or so later same problem. Any ideas????
FYI nothing plugged in yet so no load whatsoever
 
Evening all
Let’s see if anyone can solve this one.
Recently wired a new extension. Today connected up ring circuit to 32amp mcb, all relevant dead testing done ir +999mohms and ring continuity.28 .28 .48. So all good turn mcb on and pop it trips off. Rechecked testing removed sockets just to double check for any small nicks etc all fine. Reconnect and turn on all seems fine. Hour or so later same problem. Replaced mcb all fine. Hour or so later same problem. Any ideas????
FYI nothing plugged in yet so no load whatsoever
Did you conduct the figure of eight test on the RFC as a matter of interest?
 
Ir test done l-n l-e n-e.
I’m going back this morning to try and solve this, my thinking at the minute is what was previously said maybe somewhere line conductor is touching metalwork/pipework through a screw or something just strange I can’t read any sort of fault through the meter (which I know is ok)
 
Why? If the fault is occurring at 240V then the 500V test will identify it.

The op is stating that his test is not identifying the problem. 240v is an rms value and the meter is only performing a low current test. OP is fault finding, a 100v test will be more onerous on the installation.
 
So after further investigation and with earths still connected to met, an ir fault between two points is present! This is only through the the fabric of the building and not end to end of the cable. With this link out all test clear again even with earths connected to met. Mcb down rated builders need to make a decision on holes in walls and ceilings down
Hopefully that’s solved
Thanks for your input chaps
 
The op is stating that his test is not identifying the problem. 240v is an rms value and the meter is only performing a low current test. OP is fault finding, a 100v test will be more onerous on the installation.

The OP had stated that the test has not identified the problem but also that the test had been carried out incorrectly, this is not the same thing as the test not showing the fault. Now he has returned and carried out the test correctly it has revealed a fault.

Yes 240V is the rms value, the peak is around 300V, this is why we test at 500V.
IR testing is a low current test at 500V or 1000V, high current is not necessary for IR testing, it is the voltage which 8s required to stress the insulation, not current.
The insulation of T&E is only rated for up to 500V and shouldn't have a voltage higher than this applied to it.
 
Just a note original ir tests were carried out with earths connected to met. This was all clear! Since then work has carried on so this is when the fault has arisen. It was only not checked again yesterday that has caused me to only find it this morning.
 
If you have used the same batch of mcb, try and get one from somewhere else, or temporarily connect to an existing mcb as you know that one is ok as it is in use. Otherwise the problem has the symptoms of an overload despite nothing is connected. You did say it went pop first and then later reconnecting it and the it lasted an hour. So therefore it seems a wiring situation, maybe a dodgy accessory e.g socket or spur if used. On your IR test are all socket switches closed, just a thought. If you are confident in your wiring I would disconnect the accessories and then try, I know it's laborious but at least you will know. Hope this helps and please let us know the outcome as It could help me. Thanks.
 

Reply to Mcb trips but tests clear in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
332
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
654

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top