Can anyone tell me how I could have from my dead test results for a lighting circuit obtained a value of R1+R2 which is greater than my live test Measured earth fault loop impedance for the same circuit.

According to the equation Zs= Ze +( R1+R2) that should be impossible.

Any help appreciated.
 
thanks for the swift reply. but i measured and obtained 4.11 ohm R1+R2 dead test. then my live test for Zs gave me 2.3 ohm. Surely even if parallel paths exist i this should not reduce the impedance overall. these were both measured values.. It just dosnt seem to add up...pardon the pun
 
no its not a long circuit in fact its a bungalow rewire. used qite a few junction boxes. Could be a high resistance at a termination...but then how come i get a low Zs value on my final live test. Thats whats stumping me
 
In that case, and sorry to be abrupt, but can you not see you have a serious problem there??? rather than worrying about the difference between measured and calculated Zs, I'd be more worried about the fact the reading is that high at all!!

A reading that high will only get worse over time and may end up earth continuity being lost all together. All connections on that circuit need to be checked without delay for soundness.
 
whatever the case everyone i'd rather be sure and do the tests again and then systematically go through the circuit again.
Best action.
I would link the cpc and line at the db then test through the circuit and see where the resistance increases. I'd suspect it to be something like a loose cpc in a JB.
 

Reply to Measured and calculated Zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
251
Megger 15 series in my opinion are the best. Had a few 17 series that have put out err 23 codes. This is s an internal clock component issue...
Replies
2
Views
324
Darren dazz
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top