measurement of distribution | on ElectriciansForums

Discuss measurement of distribution in the Commercial Electrical Advice area at ElectriciansForums.net

P

pc electrical

could any one explain how this system works

there is 2 three phase meters, from there iv traced the cables to (1) 800a switch
how do the meters measure the 2 different loads??????

i have done a quick drawing
please see attachment

thanks
paul
 

Attachments

  • [ElectriciansForums.net] measurement of distribution
    METER FIRMIN.jpg
    39.6 KB · Views: 168
That cannot work as drawn, the Cts need to be either around the supply lines to the individual loads, or if more than one supply is present around the supply lines themselves.

The voltage inputs to the meters as well as the meter supply itself (as opposed to the current inputs) may be before or after the isolator, or even commoned where one supply is used
 
yeah what iv drawn is what i can see..... common seance tells me this can not work but it is lol there must be something im not seeing. will have to go back to factory and investigate a bit more
 
The best way is via PhotoBucket if you have an account with them. Otherwise contact one of the moderators to give you permission to upload. Your post count may be against you.

This has got me interested so would like to see the set up.
 

Reply to measurement of distribution in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Sooo the client has accepted that we don't want to be fraudulently taking electricity so that worry is out of the picture. But now basically the...
Replies
32
Views
5K
Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top