Hi can anyone give me a procedure to measure the Ze value of a house? I am currently studying to become an electrician and I am very much a rookie so please be patient with the baby step questions
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Measuring Ze value?? in the UK Electrical Forum area at ElectriciansForums.net
ok wyllis....parrallel paths is correct..and to the second question the answer is yes...both Ze and Zs are live tests but in order to eliminate parrallel paths the main earthing conductor is dropped out of the C/Us MET...under energised conditions this would be a dangerous practice as it would render the installation without a means of earthing (apart from any earth paths through bonding)....and so a safe isolation is performed first before a measured value of Ze can be obtained....I think they are lower due to parallel earth paths and it should be isolated because Ze is a live test.
as you have more that one conductor that the fault current can take....due to extranious-conductive-parts....such as metalwork bonded back to the MET....and so you have a parrallel path/s...which will reduce the impedence to any fault current....but you cant substitute bonded metalwork for a reliable means of earthing.....and likewise gas and water services that were once used as a means of earthing an install is no longer allowed......what a Ze test does is verefy that you have a reliable means of earthing of a low enough impedence to ensure that protective devices will operate within times..further more it tells you what the condition of the earthing at star is as well.....
Reply to Measuring Ze value?? in the UK Electrical Forum area at ElectriciansForums.net