Hi All,

does anyone know, when testing Ze on the Megger, and also getting the PFC at the same time, if the PFC provided is the higher of the PEFC and PSSC? ie, does it carry out both PFC tests simultaneously and provide worst case result or does it just test for the PEFC? Thanks in advance! Ps, I hope the question is clear!
 
which megger do you mean? on the 1552/3, it's a 2 wire test so you measure either pefc or pscc, 1 or the other, depending where you put your leads.assuming you are measuring Ze, then your leadsa are across L -E and so the fault current will be PEFC.
 
fail, fail and fail again.

how can you measure an accurate PFC whilst carrying out a Ze?

think about where the main earthing needs to be during Ze...then during a PEFC test...
 

Reply to Megger Question... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
223
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
683
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
625

Similar threads

Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
243
Hi all Usually I work at office or central headquarters, but sometimes I have to get on my job pants and test some Megger or show trainees or...
Replies
0
Views
341

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top