whats people's thoughts on having class 1 switches and fittings on an installation that is wired in old imperial conduit acting as the sole cpc? If there's a fly-lead from switch to back box surely this will be fine? Getting a lot of mixed anwsers on this some saying no good others saying perfectly fine? I personally think it's not a problem as conduit can be the best cpc you get. Any one else dealt with this? Thanks
 
It is perfectly fine.

It is frowned upon in certain circles, and by certain organisations, and with good reason.
The reason however is very sad.
It is frowned upon as the designers who have often little or no control over how the installation is constructed, are unable to rely on the competence of the installer to get the conduit correctly installed to provide an adequate cpc. Nothing more than that. Hence they add a secondary cpc within the containment in an attempt to ensure that there is at least one functional cpc.
Same reason that using the SWA has fallen from favour as a cpc.
It is simply that the designers cannot rely on the installer to do the job correctly so they design in some redundant safety, by insisting on additional cpc, either within the SWA or additional to.

Simply another reflection on the poor state of the competence in the installation operatives in the industry.

Note terms...
 
Last edited:
It doesn't help that the new AM2 doesn't cover conduit. It's going down the domestic route so less and less electricians are competent with conduit!!

Too true!!

[ElectriciansForums.net] Metal comduit as cpc
 
Last edited:
Just thinking back to my old foreman, he would have beaten me around the head with a large and heavy blunt instrument for wasting time and money with an earth in conduit.

PS.We didn’t have CPC’s back then!
 
I worked for a company and we worked for John Lewis, the spec was no earth wires.
No this was not in the 1960s but in 2000 in London near brands hatch.

The electrician who I worked with and was my 'mentor' said that it would have to be 'pressure tested'.
So even 'now' you do not need earth wires.
 

Reply to Metal comduit as cpc in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
273
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
267
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

  • Question
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...
Replies
8
Views
1K
  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top