OK guys, sorry for disrespect and choosing an easy path. I was writing from my phone and I was busy going out home, so I left yu just a short note.

What I want to do, is to place 16tail through the wall and under floors by drilling holes in the joints, and then to CU. I am going to use double insulated cable (standard meter tail) and secure it with 63amp fuse.

Is this ok for this kind of installation or should I use 25mm cable or sheathed cable?
 
Last edited by a moderator:
Re: Meter tail - CU >25m

3 meters max for double insulated tails, otherwise you r into subs.
No such thing as double insulated tails if you are talking about the brown/blue with grey outers.
They are insulated & sheathed.

- - - Updated - - -

OK guys, sorry for disrespect and choosing an easy path. I was writing from my phone and I was busy going out home, so I left yu just a short note.

What I want to do, is to place 60mm tail through the wall and under floors by drilling holes in the joints, and then to CU. I am going to use double insulated cable (standard meter tail) and secure it with 63amp fuse.

Is this ok for this kind of installation or should I use 25mm cable or sheathed cable?
60mm tail?...
Double insulated?...
 
Meter tail - CU >25m

The above post is making my brain hurt!! It makes no sense!! 60mm tail, 63a, 25mm cable?? Sounds like this one might need notifying to the fire service let alone a scam provider! :)
 
Meter tail - CU >25m

Going back to the tail length issue though, i was doing a bit in my parents house ( a nearly 2 year old new build) to my surprise (never noticed or paid much attention to it) the meter box was opposite side of the house to the CU, 25mm tails running through stud work, joists etc all backed up by the 100a fuse!! Length of run approx 10meters! Barratt House btw :)
 
Ideally you want to be using a SWA as your sub suitably fused at origin. This will negate the need for additional protection on your sub and also leaves you without the problem of having RCD's in series.
 
Re: Meter tail - CU >25m

OK guys, sorry for disrespect and choosing an easy path. I was writing from my phone and I was busy going out home, so I left yu just a short note.

What I want to do, is to place 16tail through the wall and under floors by drilling holes in the joints, and then to CU. I am going to use double insulated cable (standard meter tail) and secure it with 63amp fuse.

Is this ok for this kind of installation or should I use 25mm cable or sheathed cable?

Where to start.....

Firstly, there is no way that I'd run standard meter tails through the house unprotected. Secondly, do you mean "armoured" cable, when you say "sheathed"?
Are you really a qualified electrician?
 
Double insulated tails, 6181y. That's double insulation as was stated inc 3m rule for meter tails not t&e. Swa submain through a house can be hard especially if its for the whole house load. Also you need to put a sw/fuse in adjacent meter box to cut out box or in the house the opposite side of it.
The op talks and posts like someone else on here.
 
Double insulated tails, 6181y. That's double insulation as was stated inc 3m rule for meter tails not t&e. Swa submain through a house can be hard especially if its for the whole house load. Also you need to put a sw/fuse in adjacent meter box to cut out box or in the house the opposite side of it.
The op talks and posts like someone else on here.

You're right, he does sound like you :)
 

Reply to Meter tail - CU >25m in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
793
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
979

Similar threads

yeah so it looks like an old off peak heating circuit to what would have been storage heaters my preference is to remove them completely from the...
Replies
2
Views
406
I don't know if you are sorted yet but I would only do the single supply option as a very last resort. Great care has to be taken in setting up...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top