Back to the essence of it:
- 537.1.4 has not changed between red and green
- nor has 537.2.2.6
- nor has the definition of electrical installation

so I would be interested to hear the inspector's justification for a changed interpretation

Regards
Bruce
 
I think the confusion is coming from the revised regulation 537.1.3 in the BGB. The IET have now added

"Where a distributor provides a means of disconnection complying with chapter 53 at the origin of the installation and agrees that it may be used as the means of isolation for the part of the installation between the origin and the main linked switch or circuit breaker required by regulation 537.1.4, the requirement for isolation and switching of that part of the installation is satisfied"

To me that is referring to either the main cut out fuse as a fuse is classed as a means of isolation (Table 53.4) or a switch isolator that is sometimes now fitted. So to my interpretation I think it clearly outlines that provided the DNO give permission to use their fuse/isolator as the main means of isolation it clears up the single point of isolation within a house, and the fitting of extra CU's

I think that is also why we have the note now added to 537.1.3 which states A cut out fuse may be withdrawn only by a person authorized to do so by the distributor.
 

Reply to Meter Tails for new consumer unit in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
721
  • Question
Normally you'd install either a fuse-switch or a switchfuse at the incoming supply position rather than a DB, this gives you some hope of...
Replies
10
Views
1K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top