Hello, anyone know when the regs recommending a switch fuse for meter tails greater than 3m long was introduced ? On older installations (about 20 years ago) was a switch fuse required on tails over 3m ?
Thanks
Thanks
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Meter tails over 3 meters in the UK Electrical Forum area at ElectriciansForums.net
computer says 3mtr max .Think I will give the DNO a call
Only if the DNO agrees their fuse can be used.433.2.2 concerns devices for protection against overload, however the next one (433.3.1 [iii]) concerns omission of devices for protection against overload, and says a device can be omitted "where the suppliers fuse affords protection to the part of the installation between the origin and the main distribution point of the installation where overload protection is provided" (The CU in this case). So that rules that out. Looks like it is the DNO rules regarding tail length
who needs fault protection when the cable is the fuse?16mm concentric service cable to be jointed straight off a 95mm or larger main