yes pete999 tested line to earth >999 neutral to earth >999
When you swapped from RCBE to MCB is there a chance you could take an earth leakage reading, that may throw some light on the problem, as the problem is pointing to a leakage fault somewhere.
 
IR seems good so cable probably sound. If the total circuit length is great, capacitive leakage can be significant. Use a leakage clamp to measure differential current of L & N, not CPC current and report your findings, also the results for a ramp test of the RCBO.
 
I am asking if the neutral core is connected to the RCBO and not to the neutral bar, as if you have been swapping back and forth MCB to RCBO this could get missed.
If the light fittings are class II then there cannot be an earth fault there so there must be something else causing the problem.
 
This thread made me chuckle. What's been said in it could have been said in 3 posts if the OP had put all the information in to begin with.

OP, does your internet provider charge you extra for using prepositions and the like in sentences? Or where you just replying while there was water on the boil?
 
I am asking if the neutral core is connected to the RCBO and not to the neutral bar, as if you have been swapping back and forth MCB to RCBO this could get missed.
If the light fittings are class II then there cannot be an earth fault there so there must be something else causing the problem.

That is my thought as well especially if all the ir tests come back fine. I didn't mention it because he/she has ignored all my questions.
 

Reply to micc on rcbo in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Theres an FCU feeding external electric gates, an intruder alarm and I'm guessing more than 2 lighting feeds. It's been reported to the client and...
Replies
5
Views
381
Yup will do exactly that when I'm back down there. Thanks for the help
Replies
6
Views
387

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top