Mid position valve and underfloor heating

Thank you both this really helps, there are 2 micro switches,must be blind! And yes it is unvented.

Why did you disassemble the valve head in the first place?
Everything you need to access to test and diagnose the fault will be available at the joint box.
 
I'm surprised Scouse Tel isn't jumping all over this thread.

He knows all there is to know about UFH heating! ;)
 
Also when the UFHeating switch wire is disconnected from the orange, the system as it originally was works perfectly, hey ho looks like im back on site tomorrow continuing to isolate the problem.
 
If any one does have any suggestions Id be glad to get your responses, but the football is on now so wont be replying.
 
Also when the UFHeating switch wire is disconnected from the orange, the system as it originally was works perfectly, hey ho looks like im back on site tomorrow continuing to isolate the problem.

Eh? Which switch wire from which orange?

Draw out a diagram of the wiring and post it here if you want the best advice we can give.

From what you have described so far there must be 3 orange wires to fire the boiler, one from the three port, one from the ufh and one from the 2 port valve providing the positive shutoff for the unvented cylinder.
 
I'm surprised that the op didn't rip out the 3 port valve and replace with three 2 port valves?!

Or at least get the plumber to do the job right in the first place?!

It is an odd one, as they appear to have installed an unvented cylinder aswell as the ufh so the 2 port used for the positive shutoff means the plumber must have installed an automatic bypass into the system now.
The bypass isn't needed with just a 3 port as it spring returns to HW open, but you need a shutoff in the flow to the cylinder if unvented so that the flow stops if the overheat stat trips.

So all the advantages that I understand a 3 port to give have now been lost.


Bug then you can't trust a plumber to do the right or sensible thing can you?
The last Y plan system I wired the plumber had neglected to install the 2 port for the unvented or a bypass and I had to explain to him his mistake and point out the relevant parts of the MIs and draw a diagram for him!
 
If you can be bothered to reply, don't expect anyone else to!
Absolutely right ,appologies , the orange wire is from the 3 port zone valve connected to it are the input from the underfloor heating and the output to the boiler, when im calli g for heat from the ufheating the valve on hot water opens and 3 port allows the rads to heat up , its seems to be the case that when 230v is applied to the orange from the ufheating the white from the 3 port valve also livens up !
 