SafetyEICR
Just running thro some design calcs for minimum cpc size and im getting some unrealistic readings. Example 1.5mm c.s.a live and 4.mm cpc on a lighting circuit?? circuit is Zdb = 0.083
Circuit 1L1
Assuming we can use 1.5mm cpc
R1 + R2 = (12.10 + 12.10) x 1.2 x 3.57 / 1000 = 0.10ohms
ZS = 0.083 + 0.10 = 0.183
Ia = 230 / 0.183 = 1,256a
S = 1,256 squared x 0.1 = 157753 square root this figure / 115 = 3.45mm cannot be right surely??
Thanks. Does this look correct for ring circuit cpc Assuming we can use 2.5mm cpc
R1+ R2 = ( (7.41 + 7.41) / 4) x 1.2 x 7.15 / 1000
ZS = 0.083 + 0.031 = 0.11ohms
Ia = 230 / 0.11 = 2,090a
As a 60898-B 32a will trip in 0.1 at 160a this figure will be used
S = 160 x 0.1 / 115 = 0.43mm
Your fault current is not 160A though - according to your calculation it is 2.09kA!
So you need to use this - and as I said confirm with the manufacturer of the circuit breaker that it will infact open in 0.01s!
Struggling to find data for memshield mcb to see if it will trip in 0.01. Going with 0.1 as stated in regs using above calculation im getting back to using 4.0mm cpc on a 2.5mm ring main.
I think ill have to go with 0.1 as stated in regs. Circuits within mains room will have unusually high cpc due to the low impedance on the circuit. All other circuits are coming out about right.
Still getting 4mm cpc on some lighting circuits. Just doesn't happen in the real world. Although cant be marked down wrong by going with figures stated in regs!!
then you must be doing the sums wrong......
getting a 4mm cpc for a 6A lighting circuit by using the adiabatic eq. means your circuit must be 100's of metres long ?
Heres one of the calcs. assuming we can use 1.5mmR1 + R2 = (12.10 + 12.10) x 1.2 x 3.57 / 1000 = 0.10ohms
ZS = 0.083 + 0.10 = 0.186ohms
Ia = 230 / 0.186 = 1,236a
S = 1236 x 0.1 / 115 = 3.40mm
blow me over , your sums appear correct.
what is causing this calculation quirk is your Zdb being incredibly low at 0.08 , which in turn massively increases the circuits prospective fault current.
looks like you need a 4mm cpc then :-)
Yes its the lighting circuit in the main room mate. its the same for the socket circuit within the mains room. 6mm earth needed!! Assuming we can use 2.5mm cpc
R1+ R2 = ( (7.41 + 7.41) / 4) x 1.2 x 7.15 / 1000 = 0.031
S = 2090 x 0.1 / 115 = 5.74mm
I thought it was fault current squared x 0.1 and also your forgetting the square root ain't you