SafetyEICR

Just running thro some design calcs for minimum cpc size and im getting some unrealistic readings. Example 1.5mm c.s.a live and 4.mm cpc on a lighting circuit?? circuit is Zdb = 0.083


Circuit 1L1


Assuming we can use 1.5mm cpc



R1 + R2 = (12.10 + 12.10) x 1.2 x 3.57 / 1000 = 0.10ohms


ZS = 0.083 + 0.10 = 0.183


Ia = 230 / 0.183 = 1,256a


S = 1,256 squared x 0.1 = 157753 square root this figure / 115 = 3.45mm cannot be right surely??
 
Last edited:
Thanks. Does this look correct for ring circuit cpc Assuming we can use 2.5mm cpc


R1+ R2 = ( (7.41 + 7.41) / 4) x 1.2 x 7.15 / 1000


ZS = 0.083 + 0.031 = 0.11ohms


Ia = 230 / 0.11 = 2,090a


As a 60898-B 32a will trip in 0.1 at 160a this figure will be used


S = 160 x 0.1 / 115 = 0.43mm
 
Your fault current is not 160A though - according to your calculation it is 2.09kA!

So you need to use this - and as I said confirm with the manufacturer of the circuit breaker that it will infact open in 0.01s!
 
I think ill have to go with 0.1 as stated in regs. Circuits within mains room will have unusually high cpc due to the low impedance on the circuit. All other circuits are coming out about right.
 
Still getting 4mm cpc on some lighting circuits. Just doesn't happen in the real world. Although cant be marked down wrong by going with figures stated in regs!!

then you must be doing the sums wrong......
getting a 4mm cpc for a 6A lighting circuit by using the adiabatic eq. means your circuit must be 100's of metres long ?
 
Heres one of the calcs. assuming we can use 1.5mmR1 + R2 = (12.10 + 12.10) x 1.2 x 3.57 / 1000 = 0.10ohms


ZS = 0.083 + 0.10 = 0.186ohms


Ia = 230 / 0.186 = 1,236a


S = 1236 x 0.1 / 115 = 3.40mm
 
blow me over , your sums appear correct.

what is causing this calculation quirk is your Zdb being incredibly low at 0.08 , which in turn massively increases the circuits prospective fault current.

looks like you need a 4mm cpc then :)
 
Yes its the lighting circuit in the main room mate. its the same for the socket circuit within the mains room. 6mm earth needed!! Assuming we can use 2.5mm cpc


R1+ R2 = ( (7.41 + 7.41) / 4) x 1.2 x 7.15 / 1000 = 0.031


ZS = 0.083 + 0.031 = 0.11ohms


Ia = 230 / 0.11 = 2,090a


S = 2090 x 0.1 / 115 = 5.74mm
 
Yes its the lighting circuit in the main room mate. its the same for the socket circuit within the mains room. 6mm earth needed!! Assuming we can use 2.5mm cpc


R1+ R2 = ( (7.41 + 7.41) / 4) x 1.2 x 7.15 / 1000 = 0.031


ZS = 0.083 + 0.031 = 0.11ohms


Ia = 230 / 0.11 = 2,090a


S = 2090 x 0.1 / 115 = 5.74mm

I thought it was fault current squared x 0.1 and also your forgetting the square root ain't you
 

Reply to minimum cpc sizes in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
281
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
270
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
351

Similar threads

  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top