S

SafetyEICR

Just running thro some design calcs for minimum cpc size and im getting some unrealistic readings. Example 1.5mm c.s.a live and 4.mm cpc on a lighting circuit?? circuit is Zdb = 0.083


Circuit 1L1


Assuming we can use 1.5mm cpc



R1 + R2 = (12.10 + 12.10) x 1.2 x 3.57 / 1000 = 0.10ohms


ZS = 0.083 + 0.10 = 0.183


Ia = 230 / 0.183 = 1,256a


S = 1,256 squared x 0.1 = 157753 square root this figure / 115 = 3.45mm cannot be right surely??
 
Last edited:
Briggsy -

As this is just a theoretical exercise with unrealistic numbers,
are you supposed to work out the time by first using the equation in 434.5.2 and then the equation in 543.1.3?

I have just done that with the above values and it comes to 1.498.

I did it earlier with the values in your first post and it came to a similar figure 0.989 (I think)
 
Hi Geoff, I've just done the calc the way set out in 434.5.2 and it gives a much lower cpc size. Wish this was pointed out on the course!! Don't think ill have time to go back over all calcs with this method, ill just have to add a statement onto the end of the project. Thanks for your help.
 
You would need to redo the calculation with your new cpc size to confirm whether it can withstand as don't forget that the larger cpc will reduce the Zs and therefore further increase the prospective earth fault current!

Heres one of the calcs. assuming we can use 1.5mmR1 + R2 = (12.10 + 12.10) x 1.2 x 3.57 / 1000 = 0.10ohms


ZS = 0.083 + 0.10 = 0.186ohms


Ia = 230 / 0.186 = 1,236a


S = 1236 x 0.1 / 115 = 3.40mm
 
Thats it, it all seems correct, as Biff said you have extremly small Ze plus low R1+R2 by having very short circuits, where did you seen a ring 7.15 meters long and then lighting circuit 3.57meters long at the furthest point, its just unrealistic knowns used in calcs.
 

Reply to minimum cpc sizes in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
281
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
270
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
351

Similar threads

  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top