if your new work requires RCD protection in order to comply ( e.g if you are burying cable in a wall < 50mm deep etc., etc.) then you must either fit RCD/RCBO to the circuit, or an RCD FCU to your new work.
interestingly the diagram on page 425 of BGB shows socket outlets wired downstream of an FCU wired in 1.5mm....
Makes perfect sense when thought about, but woulve triggered a trip to the van to check the book if i'd found it on PIR (ECR)..!