Good Evening,
I have failed an EIC test, C1 lighting circuit has induced voltage on light switch screws.
The lighting circuit is on a split load CU non RCD side only MCB fitted.
All switches and pendants have a connected R2 however the CPC conductor present does not connect to any Earth, its floating.
The break or disconnection is probably under the floorboards.
Is there any reason why one cannot take from a tested radial socket cct, on 20A RCD, which is 1.5M distant from one of the light pendants in this failed cct, run it through the loft and connect it to the pendant ? I am told one cannot do this and the electrician wants to drill holes through the walls, run an extra CPC from the CU, up a wall surface, within trunking and tap it into one of the light switches on this circuit.
He tells me my suggestion cannot be done "the cpc must come from the same cct" Surely the many and various cpc on the other circuits are all connected to the same Earthing point so i do not see the logic in his explanation
The entire house is rewired to 16th Edition
Problem is the electricians description is a bit vague. I believe they are saying there is a cpc at all accessories but an earth fault loop test indicates 100v and subsequently will not perform the test but I could be wrong. Nine times out of ten this is an incorrectly connected cpc.
actually the description is simply that 160V is present on the fascia screws. I think i will be looking to get a second opinion and for him to quote which Regulation does not permit taking a cpc from one circuit and using it for another circuit. If it is of any value the L/E insulation test on this cct passes
, my suggestion would be to run not just a CPC but a complete new cable to the CU, and thereby isolate the faulty section completely.
this however is exactly what i want to avoid if at all possible. All cables are either under floorboards or buried and i would prefer not to have trunking running over the surfaces.
Has he verified the fault is from the consumer unit to the first light.
i personally do not think he has verified anything, i will ask him to detail what fault finding steps he has applied and what the results where, but based on his performance to date i have little confidence in his thoroughness. Incidently the cct in question incorporates a 3 way hall /landing arrangement and a two way landing/loft lighting switch arrangement.
You would prefer to have a defective cable / joint remain live and in service without knowing the nature or extent of the defect?
I have asked the electrician the following questions
Which light pendant is the first in the run (in which room) ?
have you disconnected the cpc from this pendant and at the CU and measured for continuity, what was the result ?
which wiring REG will be contravened if an earth is taken from a different circuit ?
to the first 2 there is no answer, to the 3rd there is no ref to a wiring reg, but the explanation is that if he takes a connection from the socket then somebody could in the future remove those sockets and in doing so you lose the cpc. Which of course is true, but that argument could equally apply to any other cpc if somebody decided to "remove" it.
He should be able to determine which rose is the first in the circuit, but to do this i imagine you must disconnect each rose in turn until you can measure continuity back to the mcb. If he does this and measures the associated cpc on this first run rose and it is open cct then obviously either the conductor is broken somewhere under floorboards or maybe loose at an underfloor junction box. If that is the case then either one lifts the floorboards at several places in the house to check where the cpc is lost or perhaps one can borrow another cpc. I would agree that taking the cpc from elsewhere is not the most elegant solution but lifting carpets and floorboards is a very expensive hammer to crack a nut.
in order to counter his argument about somebody removing those sockets I suggested that the incoming supply to the loft radial sockets could be cut (in between the loft joists),a junction box introduced, preferably under a loft board, the radial cct is reconnected and from the junction box run a separate cpc to either the light pendants in the loft or the light pendants for any of the 1st floor which are accessible from the loft.
I would be using using the earth from another circuit as a last solution. Someone needs to establish where the problem is as nine times out of ten it can be rectified. I suspect you are wasting your time with this electrician.
no that is not what i was suggesting, as a C1 failure it has to be resolved, my preference is for a more elegant solution than his suggestion, tacking in an extra wire via external trunking. If a cpc is derived from another cable then the induced voltage collapses and the circuit is no longer live and is safe, is it not ?
I was hoping that somebody could explain to me the electrical theory behind the assertion that one cannot take a cpc for one circuit from another circuit, all the good tested cpc's return to exactly the same point, i would think the functionality of the cpc protection is retained irrespective of the route it takes.
the problem for me is how many qualified people do I need to employ until I find one who is capable of faultfinding. If the conductor can be shown through measurement to be o/c in the leg from the consumer unit, and this cable is largely inaccessible then there are only two options open 1a) lift all the carpets, floor boards, buried trunking and run a new cable to the first ceiling rose in the loft 1b) run a new cable in external trunking to the first ceiling rose in the loft 2) take a cpc from somewhere adjacent to the first ceiling rose in the loft. What would you suggest to your customer if this was the 1 time out of 10 where it could not be readily rectified ?
if it's good enough for pefc it's good enough and label accordingly.. but wouldn't really be done in my eyes. It would be found and fixed. You could disconnect circuit from board and supply from a spur off another circuit.. and see where that leaves you.
No, not necessarily. The CPC of a cable does not suddenly go open-circuit by itself. Something is significantly wrong with that cable run, but you don't know what. You know only the symptom that the EICR has thrown up, i.e. open-circuit CPC, and you propose to alleviate that symptom by providing an alternative CPC. Anything else that is wrong will remain live and in service.
As I said back in post #6, the cable might have been partially severed by a screw or nail which is now live. Or it might contain a thoroughly defective joint made by an unskilled person using sellotape, of which one of the three cores has so far given way. Or it might have been ripped to shreds by catching on a Skil saw when somebody was cutting floorboards, and now the bare length of line conductor is resting against a non-extraneous gas pipe. You don't know whether any of these apply to you, only that the broken CPC has alerted you to a problem with the cable. Do you intend to ignore any other ramifications once your CPC is reconnected to the MET?
the proposal to use another cpc is not mine it is the suggestion of the author of the fail certificate, I am simply suggesting a less obtrusive version of his suggestion. If the conductor has been partially severed and is now live would an insulation test L/E indicate >500Meg ? The electrician has confirmed that the voltage present on the fascia screws is induced, if it really was line voltage then would not the connection of an cpc from elsewhere to this potentially partially severed cpc cause the MCB to trip ?
The gas and water/CH bonding has passed
Reply to missing lighting cpc in the UK Electrical Forum area at ElectriciansForums.net
Very technical :D
Ok I’ll try this when I’m down