Good Evening,
I have failed an EIC test, C1 lighting circuit has induced voltage on light switch screws.
The lighting circuit is on a split load CU non RCD side only MCB fitted.
All switches and pendants have a connected R2 however the CPC conductor present does not connect to any Earth, its floating.
The break or disconnection is probably under the floorboards.
Is there any reason why one cannot take from a tested radial socket cct, on 20A RCD, which is 1.5M distant from one of the light pendants in this failed cct, run it through the loft and connect it to the pendant ? I am told one cannot do this and the electrician wants to drill holes through the walls, run an extra CPC from the CU, up a wall surface, within trunking and tap it into one of the light switches on this circuit.
He tells me my suggestion cannot be done "the cpc must come from the same cct" Surely the many and various cpc on the other circuits are all connected to the same Earthing point so i do not see the logic in his explanation
The entire house is rewired to 16th Edition
I have failed an EIC test, C1 lighting circuit has induced voltage on light switch screws.
The lighting circuit is on a split load CU non RCD side only MCB fitted.
All switches and pendants have a connected R2 however the CPC conductor present does not connect to any Earth, its floating.
The break or disconnection is probably under the floorboards.
Is there any reason why one cannot take from a tested radial socket cct, on 20A RCD, which is 1.5M distant from one of the light pendants in this failed cct, run it through the loft and connect it to the pendant ? I am told one cannot do this and the electrician wants to drill holes through the walls, run an extra CPC from the CU, up a wall surface, within trunking and tap it into one of the light switches on this circuit.
He tells me my suggestion cannot be done "the cpc must come from the same cct" Surely the many and various cpc on the other circuits are all connected to the same Earthing point so i do not see the logic in his explanation
The entire house is rewired to 16th Edition