The 3 cables, one leaves clockwise, runs around 4 double sockets and returns is that a ring circuit? Then one runs as a spur heading anti clockwise to a double socket where I plug in my compressor and extractor when I'm spraying stuff. Yesterday I installed another spur through a 20amp switching box to a 16amp blue socket and plug for the chop saw but obviously it still trips. The only reason I use the 16amp circuit is because the cabeling is all 2.5 and I thot it would have to be 4 or 6 mm for the 32 amp circuit.Well the garage CU is obviously of the same era so that kind of makes sense.
But no RCD protection - not good.
Can you see how the SWA cable is terminated, has it got a proper gland? (brass thing, usually sheathed with rubber condom-like cover, grips the steel wires and usually has a brass ring tag "banjo" that earth is connected to)
I see 3 cables off the socket circuit, so it is not (all) a ring and that might be why they are on 16A and not 32A as 2.5m radials are not rated for above 20-25A depending on the thermal conditions.
Is there a ring of a few sockets and another odd socket added somewhere? Or is it 3 radial circuits?
[automerge]1590072237[/automerge]
Jeez you have given me so much valuable information, I really appreciate it. Wish you were local I'd give a good few jobs for it and the others in the house. I will double check the ring circuit by the advise and any doubts at all I will contact a proper electrician to change unit and make the necessary adjustments . Thank so much pc1966 wish everyone was as helpful as you and hope I could help others with knowledge I have too.