Go on then, I did wonder! my guess is 33k down to 11k but that's just a total guess
I am guessing it comes in at 132KV?
Go on then, I did wonder! my guess is 33k down to 11k but that's just a total guess
Sounds more likelyI am guessing it comes in at 132KV?
Those TX's sitting outside are 33kv/11kv. 132KV insulators are usually around 5' long and a little wider. Never got up close to a 440KV system I'm not authorized to work above 33KV anyway.
Inside the little building probably a couple of 11Kv to 433v transformers. Along with a small 11KV distribution system feeding other Tx's around where you are.
Even the 33/11KV transformers will probably be DYn11.
The 132/33Kv transformers I've gotten close to have all been a YNd1 vector group. Although I couldn't say if this was a common thing.
Do you cover vector groups in college?
Even the 33/11KV transformers will probably be DYn11.
The 132/33Kv transformers I've gotten close to have all been a YNd11 vector group. Although I couldn't say if this was a common thing.
Do you cover vector groups in college?
My God, you need a woman and urgently.Stayed at a hotel in Dudley last night and opened the curtains to this view this morning, i was quite chuffed then i realised thats probably a bit sad
View attachment 27982
View attachment 27983
View attachment 27984
You may not do, I only covered it during my apprenticeship properly when I started my HND.
I had been taught the concept of what they are at the training center, although it wasn't in the curriculum. (In short Star/Delta Primary or Secondary and what phase angle displacement there is).
I only learnt about how to utilize different setups from mentors at where I served my time. One use is canceling 3rd/5th harmonics resonating through a system.
It's quite an advanced subject really, if people are interested just ask away. I can see it going over peoples head quite quickly as I sometimes find subjects like this difficult to put in layman's terms.
For example a Dyn11 Tx would be....
D = High voltage Delta
yn = low voltage star with neutral.
11 = Low voltage windings are leading the primary by 30 degrees.
Correct, think of the number as a clock face 11 is 30deg lead 10 is 60 etc...
I think this is correct.
I would be interested to know why different vector groups are used in certain voltages/winding configurations/situations.
My God, you need a woman and urgently.
I think Paul wants to cover this later in his training, its a very simple voltage monitoring circuit, but once you see how it works, you will straight away understand, and will make fault finding easier
Sorry tazz I totally missed this post and only saw it when Paul quoted you!I think Paul wants to cover this later in his training, its a very simple voltage monitoring circuit, but once you see how it works, you will straight away understand, and will make fault finding easier