First of all, sorry I didn’t take more photos.
Been to a customer to price a job and had a look at his CU. Split RCD half and half.

From this picture, it appears the left hand side rcd is off, although all the circuits are powered.

[ElectriciansForums.net] Most obvious fault here


so. First thought, faulty rcd. Says it’s off but contacts must still be closed.

Further investigation. Turned all breakers off, reset rcd and it held. Tripped on test button.
Reset right hand rcd.... also held.
Turned on circuit 1, which is marked as sockets, (first one off right hand, not in picture) trips LEFT hand rcd.

Without detailing any more, it appears the left hand side bank of breakers are being supplied through the right hand side rcd. Possibly because they’ve mixed up the rfc legs. All the load on the left hand side running through one 2.5mm cable. I think I’ll clamp it out of interest.
Would this happen with just lives mixed, just neutrals, or both?

I’ll update early next week. With more photos
 
Of course it was tongue in cheek I don’t really get my hammer out I carry out correct procedure as you’ve stated as they are not meant to be disposed in general waste ?
Suffolk spark there he is thats the landlord I cudn remember he just disliked another post of mine ??
[automerge]1595800526[/automerge]
Suffolk spark there he is thats the landlord I cudn remember he just disliked another post of mine ??
Let me do an EICR on your properties and see how many I save For you
[automerge]1595800902[/automerge]
Suffolk spark there he is thats the landlord I cudn remember he just disliked another post of mine ??
[automerge]1595800526[/automerge]

Let me do an EICR on your properties and see how many I save For you
I find it funny how so many ppl say I’m too harsh but yet the first thing most properties fail on is undersized meter tails I.e service head fuse being 80a or 100a and tail size 16mm yet many sparks think this is satisfactory.
 
Last edited:
I find it funny how so many ppl say I’m too harsh but yet the first thing most properties fail on is undersized meter tails I.e service head fuse being 80a or 100a and tail size 16mm yet many sparks think this is satisfactory.

only time in 50 years in the trade in 1 shape or another have i seen 16mm tails overheat, is once, and that was a cannabis farm where not only the meter but the cut-out had been bypassed.
 
I find it funny how so many ppl say I’m too harsh but yet the first thing most properties fail on is undersized meter tails I.e service head fuse being 80a or 100a and tail size 16mm yet many sparks think this is satisfactory.

only time in 50 years in the trade in 1 shape or another have i seen 16mm tails overheat, is once, and that was a cannabis farm where not only the meter but the cut-out had been bypassed.
? yea I bet It went up in smoke. Yea I know what you mean with “it’s been fine for the past 50 years” unfortunately 50 years ago the regulations were completely different right now 16mm tails should not be covered with 80A or 100A fuses that’s the regulations. I do agree with certain things are over the top and highly unlikely to cause harm
[automerge]1595970621[/automerge]
I find it funny how so many ppl say I’m too harsh but yet the first thing most properties fail on is undersized meter tails I.e service head fuse being 80a or 100a and tail size 16mm yet many sparks think this is satisfactory.

only time in 50 years in the trade in 1 shape or another have i seen 16mm tails overheat, is once, and that was a cannabis farm where not only the meter but the cut-out had been bypassed.
I also have great amount of respect for senior sparks like yourself ?
 
Last edited:
If 16mm tails have been in use by the same occupants for 50 years without showing distress, and there hasn't been any recent drastic change such as a new electric shower added or teenage grandchildren moving in, it seems a bit harsh to give anything worse than C3.
 

Reply to Most obvious fault here in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
433
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
  • Question
I misread it.
    • Like
Replies
13
Views
946

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top