Can you use I = P/V to work out the FLA for a three phase motor if it isn't printed? If so, do you divide the power by 3 because its 3 phase?
i have got 0.63ohms written on my motor for the am2 and ive been told i need to work the overload setting out by a formula what do i do, i have to do it tomorrow
no its not, i was taught the same also. I was taught to measure current with clampmeter, and then set to 110% of that.
if you set according to FLA the windings should be protected
but the motor may be oversized and run well under FLA -so a lower setting could be used as long as nuisance is avoided
Reply to Motor Overload in the Electrician Talk | All Countries area at ElectriciansForums.net
Do you have a test meter of any kind? if so, disconnect all four wires that go into the motor and check for a low resistance between them. You...
Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...