I'm going to quote for a kitchen rewire shortly where the client is having a new kitchen fitted and new appliances and am contemplating doing away with the traditional 2.5 ring final on a 32amp mcb and running a 4mm radial instead. Clipped direct is 36amp so could still use a 32amp but with todays energy efficiency could probably even use a 20amp mcb and have the option to move up to 32 if needed.

Just wanted to see what peoples thoughts are whether anyone has done it or if the ring final in the kitchen is here to stay?
 
At the risk of sounding completely noob... I didn't even realise they did 25amp hahaha! Even better can't see newer appliances using close to that these days so that will be fine and plenty under the max carrying capacity, thanks mhar
 
At the risk of sounding completely noob... I didn't even realise they did 25amp hahaha! Even better can't see newer appliances using close to that these days so that will be fine and plenty under the max carrying capacity, thanks mhar
not all manufacturers do 25A MCBs and even those that do, rare to find them in wholesaler's off the shelf.
 
I'm going to quote for a kitchen rewire shortly where the client is having a new kitchen fitted and new appliances and am contemplating doing away with the traditional 2.5 ring final on a 32amp mcb and running a 4mm radial instead. Clipped direct is 36amp so could still use a 32amp but with todays energy efficiency could probably even use a 20amp mcb and have the option to move up to 32 if needed.

Just wanted to see what peoples thoughts are whether anyone has done it or if the ring final in the kitchen is here to stay?
Just use a standard 32Amp radial wired in 4mm2 as long as the area isn't greater than 75M2 BS 7671 App 15 can't see where the confusion lies.
 
Have done a few kitchen refurbs using 4mm radials

Especially when the entire house is on 1 ring main I take the entire kitchen off the ring main and just wire it in 1 or 2 new 4mm radials depending on loads etc

I actually quite like doing it this way
 
I often use radials domestic and commercial. There is some advantages to this. Testing is straightforward and installation in many ways. I usually do 32a. While I agree that wont work for some situations regarding C factors most of the time it does and more so for commercial. While you can do branching with radial circuits, much like the continental method I think it can become a nightmare later when additions and alterations come in to it. As well it is difficult to put three 4mm² into the terminations on sockets. It is a matter of judgement of course regards use of and future use as to whether a radial will be suitable load wise. Never had any problems so far with overloads.
 
At the risk of sounding completely noob... I didn't even realise they did 25amp hahaha! Even better can't see newer appliances using close to that these days so that will be fine and plenty under the max carrying capacity, thanks mhar

You know I was pondering whether this is a misnomer, most kitchen appliances will be no more efficient that in days of yore.

Anything with a heating element will require pretty much the same input to achieve it's purpose.

There are exceptions, obviously:-

Washing machines = wash colder
Fridges/Freezers = Better insulated.
Condenser Dryers

Things that will draw similar current:-

Oven
Hob (dedicated circuit though)
Kettle
Toaster
Blender/Mixer
Microwave
Extractor Hood
Tumble dryers

Then of course there is the multitude of crap that we never used to have.

Dishwasher
Coffee maker
Juicer
Smoothie maker
TVs
Plate warmer
Steam oven
Plinth heater
second ovens
Instant hot water taps


It would be extremely difficult to over load 4mm cable on a domestic kitchen

You ain't seen my missus attempting a Sunday roast.
 

Reply to Moving to radials in Kitchens in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
771
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top