Multiple Bonding Points on TT System | on ElectriciansForums

Discuss Multiple Bonding Points on TT System in the Australia area at ElectriciansForums.net

C

chloebear

Hi All,
I have a domestic TT installation to do on a (Very) Large house that has 5 Consumer units, due to the nature of the installation having to be done in phases it looks like it will have to stay with the majority of the boards. Anyway the question is this :- as it is such a large house would it be acceptable to have different earth spikes feeding the consumer units? i.e. probably 3 earth rods - Rod 'A' feeding two Cu's, Rod 'B' feeding 1Cu & Rod 'C' feeding two Cu's with the main bonding being taken from one of the rods?
Is this acceptable or wil it causeissues with the earth potentials?
 
Hi Chloebear,

I might be wrong but assuming that all consumer units are supplied from a single source, you should put an MET there. Presumably you have a main db feeding the sub-boards so run an earth from the MET when you run in the sub-mains.
 
Sorry, should have clarified earlier - there are two seperate feeds into the house to be brought in from a seperate PME supply. The house will be a TT system, which brings up the point of multiple earth rods - so efectivly there would be 2 MET locations.
Should the equipotential bonding to the main services only come from one MET or could it be bonded at multiple points?
 
Sorry, should have clarified earlier - there are two seperate feeds into the house to be brought in from a seperate PME supply. The house will be a TT system, which brings up the point of multiple earth rods - so efectivly there would be 2 MET locations.
Should the equipotential bonding to the main services only come from one MET or could it be bonded at multiple points?


if its a pme/tncs supply why will the house be tt?
 
The supply originally comes in to a small factory unit on the site via 3 phase - one phase has been dedicated to the house supply which is fed U/G via a 25mm SWA to the house aprox 20metres away - hence Factory is PME and house is TT. But because of a lot of historic changes to the house there has been at some time a further supply to the house hived off one of the other phases and brought in at the other end of the house to feed one of the building extensions - so 2 feeds in each at different ends of the house.
 
Thanks for the table - very useful.
Not sure what the type the existing cable feeding from the intake is, but may replace anyway. If so it would be replaced with 3 core, so including cpc, if so - does this mean that the house could become part of the PME from the factory - I was always unde the asumption that Pme was not to be exported.
 
my understanding is that you can carry over and use a cpc as long as it is at least as big as the main earthing conductor at the origin
this can include swa if big enough
then you will be able to bond as normal
and house will be at the same potential throughout
 
my understanding is that you can carry over and use a cpc as long as it is at least as big as the main earthing conductor at the origin
this can include swa if big enough
then you will be able to bond as normal
and house will be at the same potential throughout

It's not the main earth it's the main bonding that has to be the same size.
 
All exposed conductive parts of an installation have to be bonded to the main earth terminal.
So feeding another building on a pme system then any services or exposed metal has to bonded back to the met with the correct size cable, 10mm minimum depending on the origional neutral.
That's why it's sometimes easier to make it a tt system, then you only have to bond back to the earth terminal of the out building.

Hope this helps.
 
All exposed conductive parts of an installation have to be bonded to the main earth terminal.
So feeding another building on a pme system then any services or exposed metal has to bonded back to the met with the correct size cable, 10mm minimum depending on the origional neutral.
That's why it's sometimes easier to make it a tt system, then you only have to bond back to the earth terminal of the out building.

Hope this helps.


that is why i thought if you did what i said it was ok because you are providing an earth path back equal to main earth

not saying you are wrong just what i was led to belive
 
that is why i thought if you did what i said it was ok because you are providing an earth path back equal to main earth

not saying you are wrong just what i was led to belive

Yes you're right, if the cpc is the same size as the main bonding conductors (providing the main bonding conductors are the right size) then you can use this as a combined cpc/bonding conductor.
 

Reply to Multiple Bonding Points on TT System in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
842
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
965

Similar threads

It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
727
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top