Under what (if any!) circumstances is it permitted to run two separate cables to make up the conductor surface area of a larger cable (which, in this case is impossible to install...

Need to change 2 6mm radials for a single 10mm, but it's going to be near enough impossible to draw through a new cable due to lack of access to the route....

Are there any loop holes in the regs which will allow me to use the existing cables?

Excuse what's probably a really stupid question, I mainly do temp installations these days... Festival sites etc, so never have to overthink access and making do with what's already there!
 
what's the cable/s feeding? it's common to use 2 cables in parallel for distribution circuits. If they are final circuits, could yo make them into a 6mm rfc?
 
Hi - To make use of 2 conductors for 2x the current carrying capacity it’s important they both be the same length so the current is equally shared. In your case it may just be easier to run your new cable as 10mm and be done, just saying.
 
Cheers for the help everyone.

In this case, it's removing two 8.5kW electric showers (in adjacent bathrooms, being fed off the same unit, via the same route) and replacing with a single high powered unit in one of the bathrooms.

It's in T+E and both runs will be almost exactly the same length.

Considering the hassle of replacing the cables, if needs be, I'd be happy to put a small CU in the cupboard next door, use the existing cables as a distribution circuit and run a final in 10mm from that to the shower itself.

The whole RFC idea isn't something I'd considered earlier... I've never done one in anything other than 2.5mm!
 
If your calculations (accounting for installation method etc) showed that two identical cables of 5mm2 would be sufficient (for example), then if you had two cables of 6mm2 in parallel, they would be slightly overrated.

If the cables are not quite exactly the same length, the current would be shared inversely proportional to their resistances. It should be possible to work out what imbalance in lengths was permissible before one of the cables started to be overloaded due to taking too much of the current.

I'm not offering to do the calculations, but my guess is the odd few percent difference in lengths would be perfectly OK.
 
Cheers for the help everyone.

In this case, it's removing two 8.5kW electric showers (in adjacent bathrooms, being fed off the same unit, via the same route) and replacing with a single high powered unit in one of the bathrooms.

It's in T+E and both runs will be almost exactly the same length.

Considering the hassle of replacing the cables, if needs be, I'd be happy to put a small CU in the cupboard next door, use the existing cables as a distribution circuit and run a final in 10mm from that to the shower itself.

The whole RFC idea isn't something I'd considered earlier... I've never done one in anything other than 2.5mm!
what's the rating of the new shower? and the reference method that the 6mm cables are installed
 
I'd be happy to put a small CU in the cupboard next door, use the existing cables as a distribution circuit and run a final in 10mm from that to the shower itself

You don't need a CU, just a junction box. Preferably locate it so that the lengths of the 2x 6mm² runs are equal, but don't bust a gut over the last inch or two!
 
Technically it can be done, but the question is should it be done?

With parallel conductors there is always a risk that a fault on one conductor will leave the other conductor(s) overloaded. With two T&E in a house which may, or may not follow the exact same route, there is a higher chance of damage occurring to one cable than there is with cables installed for the purpose of being parallel conductors.

I personally wouldn't be inclined to do it as it is unconventional, and unconventional in a domestic installation often leads to trouble down the line.
 
if it saves a ball-ache installing a 10.0mm cable, then, although unconventional, I can see no problems as long as installed and terminated correctly, esp. to avoid overload on 1 leg, I can't see why not. notmuch different than a RFC for sockets.
 
Technically a shower on a ring ,just feels wrong .
Frugal.
(long term reliance on it's perfection -makes it dangerous)
if it saves a ball-ache installing a 10.0mm cable, then, although unconventional, I can see no problems as long as installed and terminated correctly, esp. to avoid overload on 1 leg, I can't see why not. notmuch different than a RFC for sockets.

It wouldn't be a ring, it would be a radial circuit made up of two parallel cables.
 

Reply to Multiple cables in place of one in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
310
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
932

Similar threads

  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K
  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top