Hi can any one help me been doing a lot of tests lately and found only single sockets in properties. 1 property had about 3 extension leads plugged in together running right in front of the door i put this down as a fire and trip hazard giving it a c2 am i right on this or not? thanks for your help stu
 
extensions arent usually considered fixed wiring thus are not coded in an inspection report.

but you can still write that the lack of proper sockets in the property is a cause for concern with the trip / fire hazards they may create.

so your assessment of the risks is correct , but no code.
 
No code as its not fixed wiring.

But you could add in a comment about the dangers of daisy chaining extension leads on the EICR
 
Check page 17 best practice guide 4

Inadequate number of socket-outlets. (Code C3 or, where appropriate C2, if extension leads run through doorways, walls or windows, or under carpets, or are otherwise being used in an unsafe manner)
 
Deff highlight it. Recent case of person dying in a fire. Cause of fire overloaded extension lead. Reported something like 14 appliances etc on one lead somehow. Sounds like your installation not suitable for todays requirements.
 
Deff highlight it. Recent case of person dying in a fire. Cause of fire overloaded extension lead. Reported something like 14 appliances etc on one lead somehow. Sounds like your installation not suitable for todays requirements.

I've had more than 14 items running from one 13A socket via multiple 4 gang sockets before. Not ideal I know, but the total power consumption when measured was under 13 amps. Note, I'm not saying I recommend this. And 4 way extension leads are fused - much safer than un-fused 3 way adaptors! Daz
 

Reply to multiple extension leads c2? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
567
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
760
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

  • Question
This is an interesting issue. I agree with you however I took this to task with a scam inspector some years ago and we agreed to disagree that...
2
Replies
29
Views
3K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top