Hi all
Went to a block of flats (new) to look at a job and just looked at the meter cupboard (as you do ) the top flat tails must be 8/10 m in length with no isolator just into main credit meter. 25mm on 100A supply.
My question is is there a max length for a run of tails ??
thanks john
 
Cant see anything in regs at all.
I take that they are installed in walls more than 50mm from surface or ontop of the surface of the wall. therefore not requiring a RCD.
In regards to the isolator again noting in regs.
 
yep.tails from meter to CU are your responsibility and if over 3m should be fused down to protect the DNO fuse in case mr. numpty nails the tails.
 
Just thinking as most of us may come across this situation - if we call the DNO do they have to put an isolator in (even if we supply it) free of charge as they are the only ones who can do this?

Ofcourse we can remove and replace the main fuse but the DNO dont like us doing this
 
i was talking to a meter guy the early last week....and he noticed the seals were gone on the service head.....then we got talking about working safely....now, he said if you NEED to...pull the bullit....if they see theres been recent work done (C/U change etc)...they will just replace the seal on the next visit....however, if theres no evidence of recent work having been carried out.....he said this could spark an investigation......then he had to go as he had a call through about power pinchers....third time that morning....i could hear em going on about how the police were on their way on the other end of the phone....
 
Said it before why not let the spark apply for a coded plastic seal and tell the DNO when the CU change will be changed the DNO posts it out just before the install date job done plus DNO are aware of it plus you can only replace the seal on the main fuse ie not the meter so they will not worry .

What a great idea only thing is the schemies get involved and it all turns to .........................
 
Hi all
Thanks for the replies but still unsure if there is a max length or not ?
these tails were from the supply meter on the ground floor to the various flats c/u no iso just tailed from meter to c/u. dont know how they were installed
bye the way i can guess what DNO is but what does it stand for
Thanks john
 
If you read 433.2, 433.3, 434.2 and 434.3 these specify the positioning/omission of fault and overload protection devices.

If we are installing items then we need to comply with the "no longer than 3m without fusing down" requirement, although there are a few situations where this may not be required.

As you can see from the regs if the distributor agrees that their fuse provides suitable protection from the origin of the installation then they can be a length agreed with the DNO (which is up to them) but the cables must be protected so that they are not at high risk of causing problems.

In general if they are there already and you are not changing anything to do with them leave them, if you need to change anything then fuse it down if over 3m.
 

Reply to my my what a long tail you have grandma in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
787

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top