I was just wondering with the N-E being joined at the incomer, if i was to go downstream of a circuit which was "NOT" Rcd protected and tested between Neutral and Earth that would appear as a dead short between N-E is that correct? but if i was to go downstream of a RCD protected it wont be there is at that correct? as it cant get passed the RCD is that right?

Thanks.
 
Not quite, no. An RCD is basically a measuring device, not a physical barrier (until it trips), so the N that goes in is the same N that goes out. But what you will find is that the minute you try to test the principle it will trip due to various stray currents in the system.
 
Not quite, no. An RCD is basically a measuring device, not a physical barrier (until it trips), so the N that goes in is the same N that goes out. But what you will find is that the minute you try to test the principle it will trip due to various stray currents in the system.


Yea, but why doesnt the RCD see the neutral to earth that is present at the Service point then??
 
yea i know that, but why doesnt it see that the neutral and earth are joined then? as the N has gone to E?

It's not looking for (monitoring) N to E or L to E it's only monitoring L and N for missing current.
What goes up L must come back on N, if it differs by 30ma or more (or whatever the RCD rating) the RCD will trip.
 

Reply to N-E joined at the incomer of your house in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
980

Similar threads

  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
864
If the main switch is on when testing global IR then the neutral and earth will likely give a very low reading. Not that anyone would...
Replies
10
Views
599
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top