Was putting a new concrete driveway in. And decided lights would be a good idea. So four driveway lights connected up. Quick continuity test and concrete poured. Connected up back in the house and it keeps throwing the trip. Another continuity test everything ok. Did an ir test 500v and got 0.01 across all 3 cables. Any ideas on how I went wrong and more importantly how to fix it lol
 
Monitor the IR values over the next few days and see if there's a trend of it getting better. If you believe in a higher being now would be the time to be on your knees ;)

I'm all out of magical cures but if the IR doesn't improve to around 1 Meg @ 250 volts then the only way I could suggest you might pull this out of the toilet is you may be able to convert the entire system to 12 volts depending on the fittings.
 
I wasn't thinking about transformers in the light fittings, more like one single transformer somewhere near the point of supply before your dodgy cabling disappears into the concrete and maybe 12v LED lamps (or bulbs as they're known in the UK).
 
I wasn't thinking about transformers in the light fittings, more like one single transformer somewhere near the point of supply before your dodgy cabling disappears into the concrete and maybe 12v LED lamps (or bulbs as they're known in the UK).

That's it Marvo kick a man when he's down :tounge_smile:
 
It's ok Marvo and regarding the op, he is a pillock for not doing his IR testing and i think he would agree with that.
But I do feel for the op he seems like a DOWN TO EARTH GUY :smilielol5::smilielol5:
 
Good to see Gazzer is taking all this in good humour; the Northern Irish, friendliest people in the UK I heard on the radio the other day.
OK, describe exactly what you've done, the actual bits of kit you used, etc. etc., might help to resolve the problem.
 
Agree with Archie. Also I don't know if it's been mentioned yet but if not, Split the circuit down and IR between everything it may not be as bad as it seems. You may not have to dig it all up,maybe a small section.
 
There is only 3 connections buried and I know where they are(almost) I'll give the 12v transformer ago with low voltage lamps. If not I'll get the pick out and channel the seven dwarfs lol
 
[ElectriciansForums.net] Naused it right up


[ElectriciansForums.net] Naused it right up
 
Gary just give it a couple of day's to see if the readings improve which as already been suggested. It may just yield a result for you!
 
Make sure you have checked inside the fittings to see they are not full of wet concrete!
Quick hairdryer in the fittings just in case (without melting the cables).
Getting low IR across all cores unfortunately does sound as if a connection has pulled out and been covered in concrete!

But concrete does get hot as it cures so it may dry it out, perhaps
 

Reply to Naused it right up in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...
Replies
8
Views
949
I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
Replies
20
Views
1K
  • Question
Apologies @westward10 , I did think that when I wrote it, but thought it was a catchy title! Thanks @timhoward , that does indeed sound plausible.
Replies
3
Views
962
  • Question
Please ensure that your IR test is to the Lighting Switch and NOT through their loads…!!!!! Unless of course you’ve disconnected ALL DC down...
2 3
Replies
58
Views
9K
Ok, please be aware that I am a 'do-it-yourself-er,' so if this isn't the right place to be posting this thread, let me know where I should be...
Replies
0
Views
362

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks