Hi,
First let me just say that I am not an electrician although in the past I've done the usual garage and shed wiring without having any residual issues. Second my apologies for such a long post.
However, I am now involved with something a bit bigger than a garden shed.
I am building my own bungalow and am just trying to finalise the layout of the electrics. Before anyone shouts - my big problem is that I live in Thailand and there is no code applicable to electrical wiring and from everything I've seen the professional level is not particularly high. There aren't even building inspectors to come round and check what you are building conforms with the plans let alone fits any criteria.
Given that my current house has earth cabling (in parts) but no actual ground I decided it would be a lot better if I actually tried to conform with UK regs as far as I could. So I've been having to browse the web and usually finished up somewhere in this forum.
My reason for this post is to try to get some level of confirmation to what I propose to do.
At this stage I am just listing summary points.
Electricity Supply.
I could possibly squeeze these circuits into 1 consumer unit by changing the cable layout but would prefer to use 2. Both to allow for any future changes and to retain power in parts of the house should there be an issue in one of the units.
Consumer Units. (Apologies but this is where I do get a bit confused).
First let me just say that I am not an electrician although in the past I've done the usual garage and shed wiring without having any residual issues. Second my apologies for such a long post.
However, I am now involved with something a bit bigger than a garden shed.
I am building my own bungalow and am just trying to finalise the layout of the electrics. Before anyone shouts - my big problem is that I live in Thailand and there is no code applicable to electrical wiring and from everything I've seen the professional level is not particularly high. There aren't even building inspectors to come round and check what you are building conforms with the plans let alone fits any criteria.
Given that my current house has earth cabling (in parts) but no actual ground I decided it would be a lot better if I actually tried to conform with UK regs as far as I could. So I've been having to browse the web and usually finished up somewhere in this forum.
My reason for this post is to try to get some level of confirmation to what I propose to do.
At this stage I am just listing summary points.
Electricity Supply.
- Meter is mounted on a concrete post in the road. Distance to consumer unit(s) approx 25 metres.
- Intend to use 16mm cable but will have to make sure the CU can take it.
- No earth included with supply.
- Meter is mounted on a concrete post in the road. Distance to consumer unit(s) approx 25 metres.
- 2 x 2 metre earth rods set 1 metre apart. Earth cable to be 10mm.
- Lighting circuits to be 2.5 mm with 1.5mm earth. Earth is mainly for ceiling and wall fans as I have not yet seen a ceiling light with an earth in Thailand.
- Main circuits to be 4.5mm with earth (radial).
- Air Con units are rated as less than 4kw but I have allowed one circuit for each (4.5mm with earth).
- Cooker is rated at 6 kw. Is 4.5mm cable big enough or should I use 6mm?
- Shower rooms to have water heaters rated at 6kw (max. Again is 4.5 mm cable big enough?
- Kitchen is 3.5m x 3.5 m. I am installing 4 sets of 4 sockets (mainly because I don't know what appliances will be used in what part of the kitchen apart from fridge and washing machine). I am thinking about installing a 2.5 mm ring main but again should I use 4.5mm in a ring or radial.
- The air cons (5) and water heaters (2) will all have separate circuits with 4.5 mm + earth.
- 2 lighting circuits.
- 6 main circuits.
- Total = 15 circuits.
- 2 x 2 metre earth rods set 1 metre apart. Earth cable to be 10mm.
I could possibly squeeze these circuits into 1 consumer unit by changing the cable layout but would prefer to use 2. Both to allow for any future changes and to retain power in parts of the house should there be an issue in one of the units.
Consumer Units. (Apologies but this is where I do get a bit confused).
- Power supply from meter via a 100 (or 80?) amp fused power switch into a Henley box.
- Loads to be split (and balanced) between each unit to allow power in case of issues. e.g. 1 light circuit to each unit.
- MCBs – Type B – 32amp on cooker, water heaters and main circuits. 20 amp on air cons, 6 amp on lighting and fans.
- Consumer units- 2 x 10 (possibly 12) way dual 63 amp RCD.
- RCBOs (63A/30mA) fitted on each side (4) of the consumer units.
- Power supply from meter via a 100 (or 80?) amp fused power switch into a Henley box.