Its mainly because the cable s buried in the wall now at customer request so no avoiding the rcd. I thought RCD protection was required on TL inverter regardless unless manufacturer stated otherwise if it incorporated some form of protection against DC leaking back down the circuit?
Do you always surface mount or use SWA then?
TLs do not require an rcd unless there is a reason to put one in.
The very fact it is a TL is usually the reason it needs an RCD in the first place
I Called the Napit technical team who informed me additional protection is provided by the RCD. The disconnection time of the inverter is how long it takes to shut down not how long it keeps providing power. As soon as AC is lost, the AC from the inverter is also lost.The very fact it is a TL is usually the reason it needs an RCD in the first place, and a type B at that....unless by design it can't inject DC onto the AC side in the event of a fault or whatever it states in 7671.
As far as I'm concerned, burying cables less than 50mm so that a 30mA is required is a no no if the inverter continues to deliver a hefty shock for several seconds after you've bashed a nail through the cable. The RCD is not providing the additional protection for which it is required.
As soon as AC is lost, the AC from the inverter is also lost.