Is the landlord paying for the spark but your paying for the work? If your paying you should be able to get whoever you want
Your looking for a low resistance, if you have a multifunction tester I'd advise you carry out a Zs as wellright had an hour to spare
tested from the earth point in the isolator (spot welder end) to armoured sheath and got continuity
other end tested from earth point on the fused supply to the armoured sheath and got continuity
now tested from earth point in the fused supply to the met and got continuity
my question
from the met to the earth point in the isolator (spot welder side) via a fly lead what resistance roughly if any am i looking at
all depends on the csa of the cable or the armour and it's length. figures can be obtained in the osg.
Your looking for a low resistance, if you have a multifunction tester I'd advise you carry out a Zs as well
what are you measuring? a core conductor or armour?
as i said, the resistance will depend on what you are measuring. what size MCB is feeding the circuit? e.g. if a 32A type B, then i'd expect the resistance to be less than 0.5 ohms.
so definitely less than 0.5 ohms, depending on the external Ze could be less. no way to determine without using test meter/s