Is the landlord paying for the spark but your paying for the work? If your paying you should be able to get whoever you want

landlord is paying for the check / test as weve put the new supplies in for our equipment any changes / not upto regs are coming out of my pocket

same goes if anythings wrong with his side he has to pay
 
right had an hour to spare

tested from the earth point in the isolator (spot welder end) to armoured sheath and got continuity

other end tested from earth point on the fused supply to the armoured sheath and got continuity

now tested from earth point in the fused supply to the met and got continuity

my question

from the met to the earth point in the isolator (spot welder side) via a fly lead what resistance roughly if any am i looking at
 
all depends on the csa of the cable or the armour and it's length. figures can be obtained in the osg.
 
right had an hour to spare

tested from the earth point in the isolator (spot welder end) to armoured sheath and got continuity

other end tested from earth point on the fused supply to the armoured sheath and got continuity

now tested from earth point in the fused supply to the met and got continuity

my question

from the met to the earth point in the isolator (spot welder side) via a fly lead what resistance roughly if any am i looking at
Your looking for a low resistance, if you have a multifunction tester I'd advise you carry out a Zs as well
 
what are you measuring? a core conductor or armour?
 
as i said, the resistance will depend on what you are measuring. what size MCB is feeding the circuit? e.g. if a 32A type B, then i'd expect the resistance to be less than 0.5 ohms.
 
so definitely less than 0.5 ohms, depending on the external Ze could be less. no way to determine without using test meter/s
 
I can not see any earthing conductors at the mains intake.There is nothing wrong with using the trunking and conduit as the C.P.C. but I can't see how this is earthed back to the consumer unit.
 

Reply to the thread, titled "Need Some Advice / Guidance" which is posted in Commercial Electrical Advice on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top