Hello,

I'm retired from the game but decided to drop in and ask the good folks here a few questions regarding issues a family member is having. Hope someone can help.

My wife's cousin has just signed a lease for a property.
They haven't occupied the property as it needs cosmetic work doing.

The decorator comes and plugs in his wallpaper stripper and the power trips, and keeps tripping on all the sockets he tries.
He thinks the paper stripper is faulty so buys a new one, same thing happens and happens again with his kettle and other equipment.

The electrical certificate shows test results as 'passed' with a few Zs and R1+R2 tests but shows the installation is 'unsatisfactory' One snag with that, there is nothing on the cert that explains why the installation is unsatisfactory.

I take a nosey at the sockets and there are old red and black cables mixed with new colours. At first glance it looks like a ring main. Then I remove another few sockets and there are old coloured single 2.5mm cables one the one supposed ring main.

Without testing this suggests there are two radials in one RCBO with new coloured cables added on with JB's. Both 2.5 cables at the consumer unit are red and black. The lighting circuit has three old coloured 1mm cables in one 6A RCBO. The consumer is new-ish but has been opened up that many times the fixing screws for the board face have been turned to mince meat leaving it almost impossible to gain access (took a while to remove)
This along with the new 10mm earth bond to the incoming polythene water mains pipe made me think the local handyman had been in.

It needs a rewire but the landlord insists the Electrician who issued the 'unsatisfactory' certificate give a quote along with other Electricians they've asked to quote for the job.
Is this guy incompetent or just plain lazy when it comes to filling out certificates, and would you ask him to quote for a job?

Thanks.
 
Time to come clean .... Why are you getting quotes for a rewire of a property you don't own ......

I'm retired from Electrical contracting.

My wife's cousin has signed a long term lease on the building and was hoping to open the doors in a couple of weeks.
They had the decorators in, sockets started tripping.

Calls me asking for advice. I pop over for a look and give them the gory details. The building hasn't seen an Electrician or a proper tradesman since the 70's.

The contract wanted the new occupier to pay for any building work! Solicitor should have seen the word 'Unsatisfactory' on the EICR but has admitted he missed it!!!

Now I know why they didn't get the keys to the property before they signed the contract. It's a hovel.
 
Nothing about 3 lighting cables in one RCBO, nothing about the visible damage, nothing about the installation not having a certificate even though the CU was changed, nothing about remedial work that was obvious. The visible problems alone would have set alarm bells ringing.

All I can say is that the report shows some testing. It says all testing passed. No floorboards were lifted and the condition of the installation is unsatisfactory. That's all he wrote, nothing else.
.
What's wrong with three lighting cables in one device. I've been to several properties with newish CU, where owner has no access to CU certificate, either they didn't get one or they've mislaid it, doesn't condemn the install. I don't do EICR's so perhaps not wise to comment, but I understand quite a few get down without lifting floorboards, guess its what was agreed before hand?

Edit, mistake, tis Saturday!
 
Last edited:
That still doesn't make sense - its seen an electrician recently who has done a very dubious ECIR, probably to the earlier version of the regs ....

Maybe your cousin should start again, appoint their own spark through local recommendation and get a full and proper EICR done.
 
I'm retired from Electrical contracting.

My wife's cousin has signed a long term lease on the building and was hoping to open the doors in a couple of weeks.
They had the decorators in, sockets started tripping.

Calls me asking for advice. I pop over for a look and give them the gory details. The building hasn't seen an Electrician or a proper tradesman since the 70's.

The contract wanted the new occupier to pay for any building work! Solicitor should have seen the word 'Unsatisfactory' on the EICR but has admitted he missed it!!!

Now I know why they didn't get the keys to the property before they signed the contract. It's a hovel.

Guess the only thing you can do, is pay for your own EICR, and see what you can do from there? Think telectrix would be your best bet, there are other electricians available :)
 
What's wrong with three lighting cables in one device. I've been to several properties with newish CU, where owner has no access to CU, either they didn't get one or they've mislaid it, doesn't condemn the install. I don't do EICR's so perhaps not wise to comment, but I understand quite a few get down without lifting floorboards, guess its what was agreed before hand?

????

It's simple.
If you change a CU and have three lighting circuits you should test and separate them. The handyman who installed the board didn't do that. Nether did he split the 2 radial circuits onto their own RCBO's. Instead he put them on one 32A RCBO.

3 lighting circuits on one breaker. It trips.....And you can't see, you trip and break your neck. That's why we have regulations.
 
????

It's simple.
If you change a CU and have three lighting circuits you should test and separate them. The handyman who installed the board didn't do that. Nether did he split the 2 radial circuits onto their own RCBO's. Instead he put them on one 32A RCBO.

3 lighting circuits on one breaker. It trips.....And you can't see, you trip and break your neck. That's why we have regulations.

A circuit is defined by the circuit breaker, NOT the number of cables

How do you know that 2 cables in a 32A breaker isn't a ring?
 
????

It's simple.
If you change a CU and have three lighting circuits you should test and separate them. The handyman who installed the board didn't do that. Nether did he split the 2 radial circuits onto their own RCBO's. Instead he put them on one 32A RCBO.

3 lighting circuits on one breaker. It trips.....And you can't see, you trip and break your neck. That's why we have regulations.

Okay, but if those circuits functioned as part of one area, one floor for example, that could be deemed acceptable. So to clarify, all the lighting for the property is controlled from one device?

Incidentally, you've come on here for advice, it doesn't bode well trying to be patronising, not withstanding you will get criticism. Just trying to be of assistance. :D
 
That still doesn't make sense - its seen an electrician recently who has done a very dubious ECIR, probably to the earlier version of the regs ....

Maybe your cousin should start again, appoint their own spark through local recommendation and get a full and proper EICR done.

The report was carried out last month and should have been done to the current regs as his EICR report states.

Not getting the keys before the contract is signed. The lawyer missing the word 'Unsatisfactory' on the EICR report. It's all dubious.
 
Completely unacceptable to not be allowed access and inspection prior to lease signing and would be cause to break lease in my humble opinion. If the contract is not signed then don't. For sure the building has wiring faults which may be dangerous and you / your family would be forced to fix them prior to opening for business. Ask solicitor if he'd like to stump up for the repairs bill and he might start to take an interest :)
 
There is a market for cut-price EICR. There are websites out there devoted only to offering bargain-priced reports. Sadly there are plenty of landlords who see the requirement as only an annoyance to the collection of rent, and one to be expunged at the lowest possible cost.

I've come across EICR not worth the paper they are printed out on. I can only guess that those doing these reports can't realize that they would be personally liable in court.

Landlords seem to like it.
 
A circuit is defined by the circuit breaker, NOT the number of cables

How do you know that 2 cables in a 32A breaker isn't a ring?

Have you ever rewired a property and put 3 different lighting circuits in one breaker? NO is my guess, so I have no idea what you are talking about.

The ring main isn't a ring main. It's 2 radial circuits.
70's wiring with new colour cables added by JB's, do keep up mate.
 
Completely unacceptable to not be allowed access and inspection prior to lease signing and would be cause to break lease in my humble opinion. If the contract is not signed then don't. For sure the building has wiring faults which may be dangerous and you / your family would be forced to fix them prior to opening for business. Ask solicitor if he'd like to stump up for the repairs bill and he might start to take an interest :)

Exactly! The whole thing stinks.

I suggested they null the contract and hand back the keys.
They were supposed to open in a couple of weeks, now it seems like they won't be able to open until at least February 2018.
 
There is a market for cut-price EICR. There are websites out there devoted only to offering bargain-priced reports. Sadly there are plenty of landlords who see the requirement as only an annoyance to the collection of rent, and one to be expunged at the lowest possible cost.

I've come across EICR not worth the paper they are printed out on. I can only guess that those doing these reports can't realize that they would be personally liable in court.

Landlords seem to like it.

Well said and very true. This appears to be the case my wife's cousin is having right now.

I only saw the EICR yesterday and sighed.
Gave them the low down and now a can of worms has opened.
 

Reply to Need some advice please in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...
Replies
10
Views
707
  • Question
none at all.... and the rcd trips within specification... test button operational.... nothing to suggest there's a problem until you take the...
    • Like
Replies
2
Views
614

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top