Just after some thoughts on this. I need to extend a RFC, but the Zs isn't good enough to comply (it doesn't comply currently, but it becomes my problem when I touch it). It's currently about 0.70 ohms - what I need to extend it by will be minimal, maybe taking it up to 0.75 ohms. It's protected by a C32 MEM1 RCBO, top of my head that's 0.55 ohms to meet Zs requirements. It could go on a B32 no problem - only feeding a few computers - but, they didn't make B32 RBCOs for MEM1, or if they did I can't find any in the used market.

So, where do I go from here - I can't run a new circuit, a new board is out of the question really at the minute. Does the RCD mean I only need to be looking for 1667 ohms Zs or is that all a bit naughty?

Appreciate any thoughts.
 
What is the existing Zdb and R1+R2 how does it compare with past results could be a loose/poorly tightened in one of the existing.
Since MEM 1 don't forget that we have adjusted for 230v and Cmin so once could have complied.
Whilst a stand-alone RCD can be used to overcome the high loop value I try not to rely on them in this scenario as many a time they are not tested with the test button regularly and left to stick.
How is the existing circuit wired as can additional earth be installed?
 
The cpc had an r2 of around 0.2something. It was the line that had a value of around 1.7. This is because there's a tonne of conduit and the likes on the run. I've no doubt it once complied, but I've also no doubt this RFC has been previously extended without testing by the installing company. Thing is, 0.75 ohms is a perfectly acceptable reading on a type b.
 
I have a few of the pods you are referring to.
make me an offer I cant refuse.
anything over ÂŁ300 will be instantly accepted and I will even clean the dust off.
they are all second hand and have come out of various boards i have changed.
 

Reply to Need to extend a RFC - Zs not good enough in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
I can't help wondering about earthing arrangements and how important aesthetics really are when attempting to make the best of a less than ideal...
2
Replies
21
Views
1K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top