Sounds to me as if the switch has been fed from the Fuse box with a line and neutral, so that the neon will work when the switch is on.
Sounds like it’s wired to the wrong terminals if the neon is on all the time.
Only needs the line from the switch to the contactor, if the switch is fed from the same MCB as the lighting.
 
It may be that the switch is fed from the same MCB as the shower.
In which case the neutral that needs to be used to operate the contactor is the neutral for the shower from the same MCB.
 
Yep looks like the the wires are in the wrong holes.
The black and red wires from the same cable, should be wired to the in terminals.
You really ought to sleeve the bare wires with earth sleeving and terminate them in the earth terminal.
 
The earth sleaving insulates the bare earth conductor and prevents it from coming in to contact with a live conductor when its all squashed together in the box. Ideally it should be dressed in a bit neater to help prevent this as well.

I would recomend getting the electrician to check the entire circuit to make sure the correct sized cables/contactors/fuses/MCBs are installed for each part of the circuit. It's not a common method of controlling the shower and someone could have repaired or modified it without fully understanding the implications.
 
Thanks, I'll have a chat with the electrician. I'll also get him to put some sleeving on the earth wire, wouldn't it be easier if the sleeving was already on it? Regarding the neutral wire, what would happen if it was connected up to the shower etc from the pull cord? Thanks Andrew
 
An electrician will be able to confirm about this and the neutral wiring when he checks it out. Then you know it will be nice and safe.
 

Reply to the thread, titled "Neutral wiring problem" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top