powervan

Hi whats the situation on following!
went to wire a bathroom today in old terraced property all looked good new board (last 6 months) full niceic member! certificates not to hand YET! looked in loft to find V I R cables! works out from board new cables run 2 mtrs into joint boxes picking up old cables! as it happens its not a problem for me as found a pvc 6mm left in loft and other end just outside the board:))) so can work my stuff from this BUT i would only ever connect to old cable if we were doing a rewire very shortly after!! is this a Good Practice issue or is there a reg that said THOUT SHALL NOT CONNECT TO VIR even if it tests ok?? lighting hasnt cpc but thats not the issue as this has label on the board! diff subject the plumber used a junior hacksaw to cut through a live vir cable that just had no jb on end ASSUMING it was dead( he wont do it again:)
 
VIR if not stressed isn’t a problem, the installation method may be.

We were replacing two Metropolitan Vickers open slate panels with new MCC’s. The panels and cabling were installed in 1932. Samples of the VIR were sent to BASEC to see if it was suitable for continued service. Of the 250+ motors only a dozen or so needed re-cabling. The plant is still running to this day.

Testing the cables the minimum IR wasn’t set at the stupid IET one size fits all 1MΩ. We calculated the minimum insulation resistance by using the proper method where leakage current is not to exceed 1/10,000[SUP]th[/SUP] of the circuit FLC.
To be on the safe side we lowered the maximum leakage to 1/5,000[SUP]th[/SUP] at 2X working voltage. I.E. 1000V Ph→Ph, 500V Ph→E.


You can only go by observation and testing. NOT some myth that VIR will fall apart the moment you look at it.
 
VIR if not stressed isn’t a problem, the installation method may be.

We were replacing two Metropolitan Vickers open slate panels with new MCC’s. The panels and cabling were installed in 1932. Samples of the VIR were sent to BASEC to see if it was suitable for continued service. Of the 250+ motors only a dozen or so needed re-cabling. The plant is still running to this day.

Testing the cables the minimum IR wasn’t set at the stupid IET one size fits all 1MΩ. We calculated the minimum insulation resistance by using the proper method where leakage current is not to exceed 1/10,000[SUP]th[/SUP] of the circuit FLC.
To be on the safe side we lowered the maximum leakage to 1/5,000[SUP]th[/SUP] at 2X working voltage. I.E. 1000V Ph→Ph, 500V Ph→E.


You can only go by observation and testing. NOT some myth that VIR will fall apart the moment you look at it.

Well said, that Man....lol!!
 
We have lots of vulcanised rubber in our factory connected up to fancy flush brushed chrome accessories, management won't pay for a rewire, but will pay to replace light switches, light fittings etc, we make our recommendations get over ruled shrug shoulders and accept management knows best.
 
We have lots of vulcanised rubber in our factory connected up to fancy flush brushed chrome accessories, management won't pay for a rewire, but will pay to replace light switches, light fittings etc, we make our recommendations get over ruled shrug shoulders and accept management knows best.

Best way ... then you can laugh your wotsits off at them when it all goes to rat****.
 

Reply to New board connected to V I R cables in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Often in old wiring, live to the downstairs switch, then in twin (or twin & earth) the two switched lives to the upstairs switch, and a single...
Replies
4
Views
251
downlights should be safe to do the way you are doing them having the block beside the lamp is fine as for the wire I have no clue though if...
Replies
1
Views
2K
  • Question
One route could be to call the DNO and report the unsafe install, they may decide to pull the fuses on it...
Replies
11
Views
4K
  • Question
Always do an EICR before a board change. Explain to client that remedial work, if necessary, will be charged separately. If agreed, when...
    • Like
2
Replies
32
Views
5K
Neither do I Pirate, but hey ho not to worry.
    • Optimistic
2
Replies
36
Views
9K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks