Appreciate your thoughts on this please. New build house, 1 x double garage with studio flat above. The studio flat above will be self contained with small cooker, Imm/Htr etc.
1 Phase PME supply at house. All circuits RCBO's except U/G SWA cable to garage / studio flat. SWA protected by MCB only.
Normally I would fit consumer unit in garage as per norm. But this situation, I'm thinking taking the SWA cable to consumer unit within the studio flat (on top of the garage) then from there using SWA cable to the garage protected by a MCB only.
All circuits within the flat will have to be RCD protected, but I don't want the SWA from there to the garage RCD protected. All circuits within the garage will be RCD protected. The idea being flat and garage electrically 100% separate. Person in flat will have no access to garage.
Hope it al makes sense. Thanks
 
First things first, is this garage/studio flat attached to the house or separated from the main house?? What's the size of this existing SWA cable that's been installed and how many cores??
 

Reply to New build, garage, studio flat above. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
786
Written in clauses are essential, but should be fairly standard fare to a solicitor. A similar situation exists around where I live with regard to...
Replies
9
Views
588

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top