Joined
Jun 4, 2018
Messages
10
Reaction score
0
Location
Loindon
I am currently testing a 2 bed flat, all other circuits read clear. Flat Ring not so much.

Using a Megger MFT1721

L - E Reading 300Mohms but slowly
L - N Reading 400 Mohms but slowly
N -E Reading 200Mohms but slowly

Have tried breaking the ring and narrowing down the problem but both sides come up with higher readings.

Have replaced half the ring and still no change.
Each leg reads +999
You pit a couple of sockets together it starts to drop. Tried replacing parts of ring with 2.5 to see if I can clear it but its not working.

Trying replacing a lag at a time tomorrow...

The plot is a new build so I would expect the readings to jump above 300 right away, so slow readings mean I'm having to investigate.

Does anyone here have any idea what could be causing these readings?
 
Not too sure I'd be happy with that on a rewire or new install, damp from plaster or not.
Surely this comes from the experience of un-doing all the sockets , letting them breath , getting a much better reading .. logic .
( if worried about tracking damage - I can see AFDs turning up sooner)
Is this "Damp from New Build plaster" effect common only in hot weather ?
 

Reply to New Build IR Testing RFC, can't find the issue in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
393
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
978
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
775
  • Question
https://professional-electrician.com/technical/replacing-a-consumer-unit-in-a-dwelling-niceic/ All circuits should be tested
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top