new builds with no rcd protection?!? | Page 3 | on ElectriciansForums
Discuss new builds with no rcd protection?!? in the UK Electrical Forum area at ElectriciansForums.net
michaelw6
swindon
i have recently been into a couple of property's which are apartments with no rcd protection. there are about 40 of these apartments in this block all of which i assume are the same.
i have checked the main incomer which just goes through an isolator and 80a mcb to the apartment with two supplies, these go into a quickline 2 board with two main isolators either side split peak and off peak.
with 17th edition i did not think this would be aloud.
Im requesting they change the mcbs for rcbos what are your views in case ive missed something here!
No, you can't, because you can't control who else comes into the home. No domestic dwelling can be considered to be under the control of anything other than an ordinary person under any circumstances. The guidance will confirm this.
Just playing devils advocate for one moment.....
Everyone who lives or comes into your house doesnt need to be an electrician , so long as the installation remains under the supervision of a skilled individual , which it does if a spark lives there......
yes 16th edition design i reckon.
but i dont thing there should be no rcd protection at all even 16 required some protection.
although both apartments i checked were not on ground floor...
Why does 16th require some RCD protection? There are no sockets that can supply outdoor equipment, that we know, and its not a TT system. No need for RCD. All the guys banging on about steel conduit, SELV, and cross bonding are simply complicating the matter. Its quite obviously a 16th edition install. Nowhere has the op stated they have been built since 2009. Why he doensnt know the age of the building/installation is beyond me.
well taking into consideration that you will have no skilled person. there is no paperwork with the owners or building, so no date as to when it was designed or built. and i have tried to look up age of building but no one seems to know.
so i have put in a quote to put in some rcbo,s. to satisfy 17th.
as it stands thats all i can think of doing to cover my back.
Could the properties all be 17th edition with the cables >50mm in the wall?
do you know what i never thought of that one.lol
but its been around a little while, according to the letting agents.
cheers.
some times the simplest things...
Reply to new builds with no rcd protection?!? in the UK Electrical Forum area at ElectriciansForums.net
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
I will go over and get some photos, the CU is well labelled and very long with many breakers. I never seen one that big in a small flat but then I...