New circuits wired into a plastic consumer unit | Page 2 | on ElectriciansForums

Discuss New circuits wired into a plastic consumer unit in the UK Electrical Forum area at ElectriciansForums.net

TJC1

-
Joined
Feb 23, 2014
Messages
167
Reaction score
7
Location
United Kingdom
Had to install a ring main & cooker circuit for a new kitchen we have been doing.

The consumer unit is hager split load but is plastic. There is no room in the cupboard to add another board and the customers dont want to pay for a board change.

I guess i could just note on the form saying customers did not want to change to metal?
 
This was in the draft for the 18th:
542.1.201 The main earthing terminal shall be connected with Earth by one of the methods described in Regulations 542.1.2.1 to 3, as appropriate to the type of system of which the installation is to form a part and in compliance with Regulations 542.1.3.1 and 542.1.3.2.
Additionally, there shall be an earth electrode, supplementing any earthing facility provided by the distributor, in accordance with one of the requirements of Regulation 542.2.3, to prevent the appearance of a dangerous touch voltage in the event of the loss of the main connection to Earth.
 
When plastic DBs came our they were touted as safer (no exposed metal) and more durable (don't rust). I found this acceptable then and still do. Here's a metal one that was in use till last Friday, not a good advert for metal boxes!
[ElectriciansForums.net] New circuits wired into a plastic consumer unit
I have a plastic one in my home and won't be changing it unless I have to. This was just below the ceiling in what was a hairdressers: obviously a very damp environment.
 
When plastic DBs came our they were touted as safer (no exposed metal) and more durable (don't rust). I found this acceptable then and still do. Here's a metal one that was in use till last Friday, not a good advert for metal boxes!View attachment 48256 I have a plastic one in my home and won't be changing it unless I have to. This was just below the ceiling in what was a hairdressers: obviously a very damp environment.
So you guys on here want to tell us that BS7671 Amendment 3:2015 is obsolete.
It is a responsibility of an Electrician to follow safety guidance as in the regs.and advise clients as appropriate.
 
Had to install a ring main & cooker circuit for a new kitchen we have been doing.

The consumer unit is hager split load but is plastic. There is no room in the cupboard to add another board and the customers dont want to pay for a board change.

I guess i could just note on the form saying customers did not want to change to metal?
 
Had to install a ring main & cooker circuit for a new kitchen we have been doing.

The consumer unit is hager split load but is plastic. There is no room in the cupboard to add another board and the customers dont want to pay for a board change.

I guess i could just note on the form saying customers did not want to change to metal?
Which form are you implying?
That plastic board does not comply with the current regs.i hope you have advised them.
I wouldn't do that job unless if they agree to the change of the board.
Are you signing off any certs taking full responsibility just in case something happens?
You have installed 2 circuits a rfc and cooker radial.
You need EIC and everything has to comply with the current regs.
You cannot sign of the EIC with a plastic CU.
 
Last edited:

Reply to New circuits wired into a plastic consumer unit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
441
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
793

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top