I'm working with my friend a sparky. He changed the consumer unit.

Before hand I checked all circuits for continuity and done quick eicr, everything was OK.

Now with the new board on were getting a neutral fault showing on socket ring. Funny thing is the rcd manual test button isn't working. On the rcd coving the said ring. You think it could be something to do with this why showing a fault on ring. Thank you.
 
Have you IR tested that circuit, either as part of checks before new board, or since the problem emerged?
Have you tried all circuits off and done an RCD test?
Is it a dual-rcd board - have you tried the circuit the other side - see if the problem moves?
 
The spark extended the cpc to reach the earth bar, he asked me what cpc I had on the van, I got him some off 10mm I had, if this wasn't the correct size would the cause more fault current to go through the the neutral, hence cause the test button not to work properl??
 
The spark extended the cpc to reach the earth bar, he asked me what cpc I had on the van, I got him some off 10mm I had, if this wasn't the correct size would the cause more fault current to go through the the neutral, hence cause the test button not to work properl??
What do you think?
Don't confuse yourself pal, you have two issues here -
1 - does the RCD work or not
2 - why does one circuit cause the RCD to trip

Sort out number 1 first and get the board happy with that circuit disconnected.
Then move onto sorting out number 2. IR tests are your friend, L+N to E.
 
What do you think?
Don't confuse yourself pal, you have two issues here -
1 - does the RCD work or not
2 - why does one circuit cause the RCD to trip

Sort out number 1 first and get the board happy with that circuit disconnected.
Then move onto sorting out number 2. IR tests are your friend, L+N to E.
You asked me what im thinking.

The spark has extended the cpc using the wrong size cpc causing more fault current to go through the neutral. Causing the test button not to work.
If I change the cpc to the correct size the fault current will go to earth, the neutral will be what it should be, the test button will work.
Thats what I think.

Thats what ill be doing 1st thing Tuesday
 
Assuming the earthing conductor should have been 16.0 replacing a short section with 10.0 will have a negligible effect. You have a neutral to earth fault on the ring final so why would a reduced earthing conductor change this.
 
What do you think?
Don't confuse yourself pal, you have two issues here -
1 - does the RCD work or not
2 - why does one circuit cause the RCD to trip

Sort out number 1 first and get the board happy with that circuit disconnected.
Then move onto sorting out number 2. IR tests are your friend, L+N to E.

What do you think?
Don't confuse yourself pal, you have two issues here -
1 - does the RCD work or not
2 - why does one circuit cause the RCD to trip

Sort out number 1 first and get the board happy with that circuit disconnected.
Then move onto sorting out number 2. IR tests are your friend, L+N to E.

Assuming the earthing conductor should have been 16.0 replacing a short section with 10.0 will have a negligible effect. You have a neutral to earth fault on the ring final so why would a reduced earthing conductor change this.
No larger cpc that is required, if you read what I put he's put 4mm cpc on a circuit that should be 1.5mm. Does the cpc not need to be the correct size.
 
the extended cpc has nothing to do with it. you have a N-E fault on the ring circuit which is inhibiting thr RCD. i don't know the theory behind this but i've had it a couple of times.
 

Reply to New consumer unit install issue. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
223
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
683
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
625

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top