I'm working with my friend a sparky. He changed the consumer unit.

Before hand I checked all circuits for continuity and done quick eicr, everything was OK.

Now with the new board on were getting a neutral fault showing on socket ring. Funny thing is the rcd manual test button isn't working. On the rcd coving the said ring. You think it could be something to do with this why showing a fault on ring. Thank you.
 
I read that you can get a error from neutral to protective earth if the cpc is oversized.

the extended cpc has nothing to do with it. you have a N-E fault on the ring circuit which is inhibiting thr RCD. i don't know the theory behind this but i've had it a couple of times.
OK what do I do then, I had all the sockets off, Its passing I.r. what you suggest?
 
OK what do I do then, I had all the sockets off, Its passing I.r. what you suggest?
Its not the "oversized" cpc. You've been told that. Have you measured earth leakage from the circuit whilst energised? Have you done an IR test of the circuit to the MET, have you ensured the neutrals are in the correct bar. Have you split the circuit in half and tried energising 1 leg?
 
No he's grabbed the money, ----ed off, saying he's busy.

He's been paid for the job despite it not being complete? And left his trainee to fix it? Why did the customer pay him before the job was finished?

Are we getting the full story here?
 
Now with the new board on were getting a neutral fault showing on socket ring.

OK what do I do then, I had all the sockets off, Its passing I.r. what you suggest?
In your OP, you say there is a neutral fault. Later you say the circuit has passed IR. Please can you explain this, so we are better placed to advise?
 

Reply to New consumer unit install issue. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
244
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
717
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
686

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top