Thats exactly how most of the older terraced houses round my way are as well. How will you test it to confirm it's TNS or TNC-S?

as Dave says in #27. I did get caught out once by the nic bloke, to be fair it said pme on the head, but the readings were different and he insisted it was split concentric.
 
I meant to add as we need to test Ze and PSSC then it makes sense to do these tests together, before reconnecting the EC and the doing your Zdb and the other PFC measurement.

Plus I would have done a Ze test at the pre-test stage before even quoting a price ;)
 
Well I check them at the same time, obviously because I am checking Ze the main switch is off anyway, and in domestic the tails are usually fairly short and I am testing from the live side of the mains switch, and with only a short run for the 16mm EC it makes no practical difference.

Bearing in mind this test (for TNC-S v TNS) is only really necessary on the odd occasion where it could be an either/or situation

Sure, only required if it's not clear by inspection. But a while ago I saw a head that looked like TN-C-S, but when opened up (not by me), was clearly TN-S, supplied using split concentric underground cable.

Just thought that although different values of PEFC and PSCC say 'TN-S', similar values don't necessarily mean 'TN-C-S'. In which case, a direct resistance check may decide the matter.


Edit: And yes, agree, if testing PEFC (and Ze), you'd test PSCC (and Z line) at the same time, anyway.
 
Last edited:
Yes agree HS, sometimes it is not clear, but then again I always carry out a few essential pre-tests before I give a price, which the OP clearly hasn't :), one day he will regret not doing a few preliminary tests and checks before quoting :) and this will end up biting him on the arse one day, can you guess why I always pre-test now ? ;)
 
Hmm . not sure about TNCS/PME as already said test the Zs and Zp-n , I wouldn't be quoting until that and the preliminary testing of the circuits is done along with the usual visual checks , or you could get yourself in deep s--t .give them the quotation of all that you find..
 
Same in the flat i live in. A service head in each flat with the MEC connected in to the side of the cutout. The cutout is fed from a split concentric from a TP service head in the basement which is PME.

It can get awkward on flats such as yours because the incoming supply DB can be TNC-S at the incomer, but each flat is technically TNS as a separate dwelling/installation in it's own right, although for bonding requirements and certification purposes are treat as TNCS/PME

I had some documentation from UKPN which goes into far more detail into these "hybrid systems", for us though they are treat as TNC-S according to UKPN.
 
It can get awkward on flats such as yours because the incoming supply DB can be TNC-S at the incomer, but each flat is technically TNS as a separate dwelling/installation in it's own right, although for bonding requirements and certification purposes are treat as TNCS/PME

I had some documentation from UKPN which goes into far more detail into these "hybrid systems", for us though they are treat as TNC-S according to UKPN.

Yeah i have 10mm bonding in the bathroom to water pipes which are fed from a plastic incomer from the street. Never tested it to see if its actually extraneous though.
 
Yeah i have 10mm bonding in the bathroom to water pipes which are fed from a plastic incomer from the street. Never tested it to see if its actually extraneous though.

These really blur the lines, because you only have one origin (the incoming supply) usually with one CNE link at the origin and separate earths at each flat, but then according to BS7671 each dwelling is classed as a separate installation, however the gas and water services are distributed and shared as well.
So we end up with a hybrid system, and the DNO make the rules, their supply, their rules.

If you search for the UKPN documents on line they are free to download, but they can be a bit boring to read lol.
 
These really blur the lines, because you only have one origin (the incoming supply) usually with one CNE link at the origin and separate earths at each flat, but then according to BS7671 each dwelling is classed as a separate installation, however the gas and water services are distributed and shared as well.
So we end up with a hybrid system, and the DNO make the rules, their supply, their rules.

If you search for the UKPN documents on line they are free to download, but they can be a bit boring to read lol.

Something i was wondering regarding Ze/Zdb. i have a service head in my flat which is fed from the TP head in the basement. Is it technically Zdb from my service head and not Ze?
 
Something i was wondering regarding Ze/Zdb. i have a service head in my flat which is fed from the TP head in the basement. Is it technically Zdb from my service head and not Ze?

According to B7671 with each flat being a separate installation it would be Ze, however as already said with this being a hybrid system then technically it would be a Zs.

About as clear as mud lol, if I was filling in an EIC sheet for say a CU change I would put it down as Ze for your flat.

The DNO class it as TNC-S/PME for bonding purposes as this is still the most onerous situation in the event of a broken suppliers N to the TNC-S/PME head at the origin, so I can see why they class it as such.
 
Something i was wondering regarding Ze/Zdb. i have a service head in my flat which is fed from the TP head in the basement. Is it technically Zdb from my service head and not Ze?

i suppose it's what you define as the source of the installation. the TP head or your 1P head. as the TP head is technically outside your home, then you could say that the source of your installation is your head.
 
You are all saying that I have not carried out and pre tests, true I haven't but what makes you think I am not going to? I always very time test it to death, read all my previous posts regarding board changes over that last two years on here and you will see I always pre test.

I actually said earlier in this thread I am going next week to do all the pre tests before I change it.

You are suggesting you cannot even quote before doing this, I always give a ball park figure subject to various things, noses they agree to that why on earth would I waste my time pre testing it to then quote.

So just to set the record straight..

I always pre test every time!
 
Yes agree HS, sometimes it is not clear, but then again I always carry out a few essential pre-tests before I give a price, which the OP clearly hasn't :), one day he will regret not doing a few preliminary tests and checks before quoting :) and this will end up biting him on the arse one day, can you guess why I always pre-test now ? ;)

I always pre test a board every single time thanks, but no, not once have I pre tested it before quoting ad that's just stupid in my opinion, at least get them to agree to a price subject to conditions that you explain to them first.
 

Reply to New Consumer Unit in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
510
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
981
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
909

Similar threads

Only his early stuff.never muched like any stand up comedians .although the only one I've seen live was Roy chubby brown in the 90 s .can't say I...
Replies
11
Views
508
However it's done, you need to have a guarantee of no sharp/unprotected edges that can damage the insulation. Personally, I'm not that impressed...
Replies
2
Views
533

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top