Trainee question! Would I be right in saying that although it's TN-C-S it might not necessarily be PME?

True, but I think if you ring WPD they will say all TNC-S is now PME, I just call it the same, because it generally is as far as I am concerned.
 
Unfortunately this is a mid terrace, quite an old property, probably 1930 I think, no access either side due to neighboring houses.

Its kind of a non starter, plus the bathroom and kitchen are both downstairs at the back of the house which is quite deep front to back and no water at all in the rest of the house, so would literally have to go from front to back and probably trash half the house in the process.

View attachment 27753

could well still be TNS even though it looks like TNC-S.
 
Your average 1930's built house is going to have suspended floors downstairs and T&G floorboards both up and downstairs, so spring a few floorboards and run a 10mm bond to where you need it.

This is of course assuming you have already confirmed that bonding is actually required in the first place?

There are a lot of 1970/80's terraces and wimpey homes around here which follow the basic layout of gas and electricity by the front door and water main under the sink at the rear of the house with 6mm main bonds. The water main is however a black plastic pipe and rarely actually requires a main bond in the first place so I am normally perfectly happy leaving it as it is.
 
Looked at the pic, IMO if the 6mm bond is mech okay and no thermal damage leave it. Measure it as well for piece of mind. (you know the value you are looking for.)
 
Trainee question! Would I be right in saying that although it's TN-C-S it might not necessarily be PME?

You are right in saying that yes, all PME supplies are TNCS but not all TNCS supplies are PME. for a start there is a system called PNB (protective neutral bonding) which has just one N-E connection via an earth electrode wheras PME has multiple earth electrodes.

True, but I think if you ring WPD they will say all TNC-S is now PME, I just call it the same, because it generally is as far as I am concerned.

That is a brilliant answer to give to a trainee asking a reasonable question!
 
You are right in saying that yes, all PME supplies are TNCS but not all TNCS supplies are PME. for a start there is a system called PNB (protective neutral bonding) which has just one N-E connection via an earth electrode wheras PME has multiple earth electrodes.

That is a brilliant answer to give to a trainee asking a reasonable question!


Is the earthing requirement different for PNB & PME? I cant see that it would be.
 
Last edited:
I have a consumer unit to change, the earth on the gas is easy enough but the water is in 6mm and literally the other end of the house and would be a nightmare running in a new cable

Just to add, it is green and yellow, so not like its just green.

Your average 1930's built house is going to have suspended floors downstairs and T&G floorboards both up and downstairs, so spring a few floorboards and run a 10mm bond to where you need it.

This is of course assuming you have already confirmed that bonding is actually required in the first place?

As davesparks says, see what the ground floor construction is. If suspended floor, then it may be easy. In fact, since the existing cable isn't the original you might find that you can use it as a pull through.
 
Yes it could be split in the head, without measuring it I dont know.

The floor in the front room is suspended but the middle room and kitchen appears to be solid unfortunately.

yes I accept its not a very accurate answer to give a trainee.
 
Yes it could be split in the head, without measuring it I dont know.

The floor in the front room is suspended but the middle room and kitchen appears to be solid unfortunately.

yes I accept its not a very accurate answer to give a trainee.

Thats exactly how most of the older terraced houses round my way are as well. How will you test it to confirm it's TNS or TNC-S?
 
By comparing Ze and Zp-N, if the readings are identical then it will be TNC-S, this is because of the CNE link in the head and the PEN conductor are common to the N and E.

Anyone tried checking for TN-C-S / TN-S by measuring the resistance between the incoming neutral at the first accessible point (assuming reasonably close) and the earthing terminal on the head?

Main switches all off, so no current flow and check for any voltage, just in case.

I would have thought that this might be a more reliable and direct way of telling? Clearly if there's any significant voltage or resistance between these points, then there's no local connection between the two.
 
Anyone tried checking for TN-C-S / TN-S by measuring the resistance between the incoming neutral at the first accessible point (assuming reasonably close) and the earthing terminal on the head?

Main switches all off, so no current flow and check for any voltage, just in case.

I would have thought that this might be a more reliable and direct way of telling? Clearly if there's any significant voltage or resistance between these points, then there's no local connection between the two.

Well I check them at the same time, obviously because I am checking Ze the main switch is off anyway, and in domestic the tails are usually fairly short and I am testing from the live side of the mains switch, and with only a short run for the 16mm EC it makes no practical difference.

Bearing in mind this test (for TNC-S v TNS) is only really necessary on the odd occasion where it could be an either/or situation
 

Reply to New Consumer Unit in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
275
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
779

Similar threads

If two tariffs are sufficient, and you don't need too many ways, you can easily add an SPD kit to the Fusebox F2014DT dual tariff board. The only...
Replies
1
Views
301
Yes that does appear to be the case. I may get an electrician to fit the correct glands. Thank you.
Replies
10
Views
454

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top